davino

can somone tell me how to mesure pfc for a domestic property need this asap!!!!!
thanks in advance
 
Disconect Main Earth. Put meter across Earth incoming (met) Connect other leads to Phase conductors do test. Then connect Earth and Neutral test leads together and connect to neutral phase conductor, connect the other lead to Line Phase conductor.
Test again. Wich ever is the highest reading in Ka record that on the test results.
Don't forget to re connect the main Met.
All these tests done with power on cons unit OFF
 
Last edited by a moderator:
You could also buy Guidance Notes 3 it will help you with all aspects of Testing & Inspecting
 
Disconect Main Earth. Put meter across Earth incoming (met) Connect other leads to Phase conductors do test. Then connect Earth and Neutral test leads together and connect to neutral phase conductor, connect the other lead to Line Phase conductor.
Test again. Wich ever is the highest reading in Ka record that on the test results.
Don't forget to re connect the main Met.
All these tests done with power on cons unit OFF


under what function do i set the tester?? i have a metrel 2100 easytest...thanks

You could also buy Guidance Notes 3 it will help you with all aspects of Testing & Inspecting


thank frank i think i will!!
 
Last edited by a moderator:
Sorry not familiar with that test set. I use Fluke 1653. But when I had Robin test kit
if I remember correctly it was the loop meter that was used for Ze and Prospective fault current. I'm sure if that's wrong a user of Robin kit will correct me
 
set your earth fault loop impedance tester to 20KA and dependent on whether you have a 2 lead or 3 lead tester you connect (3lead) green and black to neutral and red to live this is your potential short circuit current (pssc) then connect green and black to earth and red to live this is your prospective earth fault current (pefc)or (pfc) it states that you must determine the pefc and pssc at every relevant point in the installation this can be done by calculation as laney06 describes or measurement or enquiry hope that helps you.
 
Disconect Main Earth. Put meter across Earth incoming (met) Connect other leads to Phase conductors do test. Then connect Earth and Neutral test leads together and connect to neutral phase conductor, connect the other lead to Line Phase conductor.
Test again. Wich ever is the highest reading in Ka record that on the test results.
Don't forget to re connect the main Met.
All these tests done with power on cons unit OFF


Why do you need to Disconect Main Earth for the pefc test?
 
Ohms law applies to DC supply & not AC

although the ballpark figure won't be far off, it still isn't entirely accurate
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Prospective fault current
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
34

Advert

Thread statistics

Created
davino,
Last reply from
brucelee,
Replies
34
Views
50,047

Advert

Back
Top