Can anybody give me the definitive answer to the question of why on TNCS earring arrangement when testing Pefc and Pssc sometimes the values are different? When we are essentially testing down the same path as the earth conductor and neutral are combined? And therefore both share the same parallel paths etc.
 
Last edited by a moderator:
Can anybody give me the definitive answer to the question of why on TNCS earring arrangement when testing Pefc and Pssc sometimes the values are different? When we are essentially testing down the same path as the earth conductor and neutral are combined? And therefore both share the same parallel paths etc.
Think of the supply cable, it shares a characteristic with T&E in so much as the CPC strands of either the PEN/CNE cable can be of a lower CSA than that of the line conductor, same can be said about the tails.
 
Think of the supply cable, it shares a characteristic with T&E in so much as the CPC strands of either the PEN/CNE cable can be of a lower CSA than that of the line conductor, same can be said about the tails.
Yes I understand the difference in size of the conductors but if the earth and neutral are combined I.e. connected in the cut out then surely the only difference is the size of the earthing tails conductor which at a length of say max 3m’s should be negligible.
So line to earth (CNE)
Or line to live (CNE)
Share the same path?
this is where I get a little confused.
 
It's easier to compare the the Ze and the impedance of the return path from phase to neutral (which on my MFT you have to do first anyway) and see whether the csa difference reasonably accounts for it.

Mathematically, a difference of 0.01 ohms between the two makes a much bigger difference to the calculated PEFC and PSCC.
To get the idea do 230/0.05 and 230/0.06 and see the difference 0.01 ohm makes.
 
It's easier to compare the the Ze and the impedance of the return path from phase to neutral (which on my MFT you have to do first anyway) and see whether the csa difference reasonably accounts for it.

Mathematically, a difference of 0.01 ohms between the two makes a much bigger difference to the calculated PEFC and PSCC.
To get the idea do 230/0.05 and 230/0.06 and see the difference 0.01 ohm makes.y

makes sense now thanks for the replies.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Pscc and Pefc
Prefix
N/A
Forum
Electrical Testing & PAT Testing Forum
Start date
Last reply date
Replies
5

Thread Tags

Tags Tags
pefc pscc

Advert

Thread statistics

Created
Bsharp,
Last reply from
loz2754,
Replies
5
Views
2,298

Advert

Back
Top