Can anybody give me the definitive answer to the question of why on TNCS earring arrangement when testing Pefc and Pssc sometimes the values are different? When we are essentially testing down the same path as the earth conductor and neutral are combined? And therefore both share the same parallel paths etc.
 
Last edited by a moderator:

Lister1987

-
Trainee
Esteemed
Reaction score
1,503
Can anybody give me the definitive answer to the question of why on TNCS earring arrangement when testing Pefc and Pssc sometimes the values are different? When we are essentially testing down the same path as the earth conductor and neutral are combined? And therefore both share the same parallel paths etc.
Think of the supply cable, it shares a characteristic with T&E in so much as the CPC strands of either the PEN/CNE cable can be of a lower CSA than that of the line conductor, same can be said about the tails.
 
OP
B

Bsharp

-
Reaction score
18
Think of the supply cable, it shares a characteristic with T&E in so much as the CPC strands of either the PEN/CNE cable can be of a lower CSA than that of the line conductor, same can be said about the tails.
Yes I understand the difference in size of the conductors but if the earth and neutral are combined I.e. connected in the cut out then surely the only difference is the size of the earthing tails conductor which at a length of say max 3m’s should be negligible.
So line to earth (CNE)
Or line to live (CNE)
Share the same path?
this is where I get a little confused.
 

timhoward

-
Esteemed
Arms
Reaction score
7,896
It's easier to compare the the Ze and the impedance of the return path from phase to neutral (which on my MFT you have to do first anyway) and see whether the csa difference reasonably accounts for it.

Mathematically, a difference of 0.01 ohms between the two makes a much bigger difference to the calculated PEFC and PSCC.
To get the idea do 230/0.05 and 230/0.06 and see the difference 0.01 ohm makes.
 
OP
B

Bsharp

-
Reaction score
18
It's easier to compare the the Ze and the impedance of the return path from phase to neutral (which on my MFT you have to do first anyway) and see whether the csa difference reasonably accounts for it.

Mathematically, a difference of 0.01 ohms between the two makes a much bigger difference to the calculated PEFC and PSCC.
To get the idea do 230/0.05 and 230/0.06 and see the difference 0.01 ohm makes.y

makes sense now thanks for the replies.
 

Reply to Pscc and Pefc in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi gents and ladies, I’ve just bought a Kewtech KT63, the instructions aren’t very clear on lead setup. When doing a Ze is this a 3 lead test on...
Replies
3
Views
1K
Hi everyone Recently I have come across an advert of someone selling Afdds C type and the person mentioned the need to sell because Zs was too...
Replies
16
Views
2K
Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V...
Replies
5
Views
659
I was asked to go and take a look at a generator set up by a marquee company yesterday to do some testing. It was a brand new JCB 65QS with...
Replies
7
Views
1K
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
511

New Posts (Please Reply)

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Top