Search for tools and product advice,
Discuss Question - British Gas engineer says there is a fault ? in the Central Heating Systems area at ElectriciansForums.net
Sch123
Firstly I don't know if I'm allowed here as I am not an electrician
I have a question though....
Just had british gas out here to service my boiler
He refused to carry out service because voltage stick glowed when he touched the casing on speaking with another gas engineer he tells me that as 240 volts go through the boiler then the voltage stick may just light anyway.
You can touch the casing without any ill effects
On speaking with British Gas engineer, he then put a meter into one of my upstairs sockets and said it read 100 oms and that this would be classed as dangerous, quickly followed by he isn't an electrical engineer.
Obviously this has made me worry as reading was in my sons bedroom.
my questions are...
1. The volt stick is it a true indicator of fault?
2. Is 100 oms too much for a plug socket and if so how dangerous?
3. As plug sockets and boiler on 2 separate rings then how can there be a fault on both?
Hi Sarah,
Welcome to the forums.
Voltsticks are not a reliable method of establishing whether there is a dangerous voltage present. I suspect most of us have them, but as stated, they should not be considered reliable. I typically use mine for locating cables and for general 'is it dead' when trying to find which fuse supplies an unidentified cable (where I don't yet know where that cable goes exactly) but I would not stake my life on one as such my voltstick is rarely used.
To test whether the boiler casing was live, I would use a different piece of equipment like an approved voltage indicator which actually makes contact with the metal and a series of tests between the case and the various conductors of the supply cable (or nearby metalwork such as the sink or other piece of electrical equipment). Waving a voltstick around the metalwork could yield all sorts of spurious results. It is quite common for ghost voltages to be found on cables and equipment, these are usually induced in the cable by induction or capacitive coupling where cables run next to each other (as they often do) but these will quickly disappear when the right test equipment is used.
The 100 ohms... without knowing exactly what he said and what 'meter' he used, it's hard to be certain. But if he is referring to what is called the earth fault loop impedance, then you may have a problem that will require intervention from an electrician. But this is only a 'may'.
As for why there could be a fault on both... the 100 ohms may not actually be a fault. Certain types of earthing can result in high earth fault loop impedances and can be mitigated by good design of the installation. And as stated, the voltstick lighting up just inidcates it picked up an electric field of sufficient strength to turn it on. It may not be a fault at all.
The best advice is find a local electrician and have them come and check it out. You should get some recommendations from family, friends and colleagues for a local electrician (that they have used and been pleased with) and have them come and check these two issues out.
BG now there is a name to conjure with, volt sticks are a waste of space and should never be used for testing purposes, sent you a PM. Anyone nearby able to help?
BGs' standard socketnsee tester gives a rough guide to values. As to whether it is unsafe would require an electrician to determine. A couple of tests and visual should not take more than an hour. The remedy if there is a fault is not known, as to cost or whatever. But if you get it checked you could always tell us on here what was said/recommended and we could probably tell you if that is valid or fair. Maybe a pic or two would be a great help.
P.S. And yes you are allowed on here and welcome:)
Well there is nothing to see really without me taking face plate off its a new socket I had then changed as none of the existing sockets had switches on them - spoke to BG to complain was told that the call centre operative was qualified to make a judgement call on whether this was correct or not because he used to be a carpenter on a building site for 3 years and continued to tell me BG would not come out to the boiler again until they had an electricians report and he would not escalated my complaint .... I have no words... finally got through to a woman who was a lateral thinker and within a couple of minutes she offered me a good will gesture of £30 not to take complaint further. However I declined the offer any BG say its now in the system and will be addressed within 8 weeks.
I just realised this man must have been into the boiler anyway despite his nonsense about whether or not the volt stick was red or not because he had asked me to run the hot water and the pressure gauge is inside my boiler you have to open the flap to see.
Sarah, if, and I say if the BG engineer thinks the zs for a socket circuit is around 100 ohms, this could be an acceptable reading if your property is a TT supply (this means you should have a rod in your property somewhere acting as the earth).
It may be prudent to find a local spark to come and do some very basic tests on the incoming supply and the socket circuit. This could be done in an hour and a small price to pay for piece of mind.
Ask around your friends and neighbours to see if they can recommend somebody
IF you can post your rough location there might be a forum member close by that can take a look.
If your meter and distribution board is for example in your hall Sarah have a look outside the door and see if you can see some round green and yellow cable which would go to a copper rod buried in the ground. If this is the case your 100 ohms is perfectly acceptable - providing you have RCD protection on all circuits in your house.
What would a rod look like :)
I'm in HA2 I know every type of contractor but not an electrician how totally inconsiderate of my friends for one of them not to be a sparky ;)
A copper rod would be quite long but it will hammered into the ground, should be about 3/8" in diameter with a green and Yellow cable attached to it, by the look of your location it would unlikely your house would have one, but have a look in any case, check close to the area outside near where you Fuse board is on the inside. Better still a picture of the electric meter area should tell us something.
Do you have the report in writing?
How about contacting BG and tell them that you believe their engineer was scare mongering. Tell them that you will get an qualified electrician in to test what their engineer has told you. Ask them that if the tests contradict what their engineer has said are they willing to pay for the test?
Good idea Spoon, trouble is bg wouldn't know what an EIC oR EICR is cus their "engineers" are never wrong, at least not in their eyes, I can't believe the Muppet's actually entered "volt stick fail" in writing, mind boggling incompetence on this Blokes part. I wish I had some clout in this industry, I would tear them an extra one.
If their engineers are never wrong then they wont mind saying they will paying for the test if it contradicts their engineer, as what their engineer says must be true and the test will not contradict what he said.
Too deep for this time of night Spoon, I'll only get a Migraine
I get sick to the teeth of the BG cowboy company co'ercing their "engineers" telling people with perfectly safe TT installations that their electrics are dangerous
The experience of going to a number of properties where the householder has been scared rotten by these untrained charlatans seems to be blatant incompetence or if not one big national money making scam
They thrive on being a past nationalised industry where trust was given because a high standard of service was the norm
That about sums it up.
I had a customer just before Christmas ask me if I'd be prepared to rewire a relatives place because a BG engineer had condemned the installation.
BG's aggressive,sales driven policy of condemning,fault-free installations,is something i have described,many times,over the last 10 years.
I fully expect it to be the PPI job,of the future.
All that would take,would be a list of people,who believe they were wrongly sold,over-priced and un-required services,and one or more ex-employees,at higher level,to confirm this,as a policy :)
I remember a British Gas engineer telling the tenant her rcd was faulty.
He had carried out a zs test inside the boiler but every time he tried to do the test the rcd would trip.
He must have never heard of a low current zs test.........
I am not sure what type of bird it was...but it's bill was massive :):)
(Which is only funny,if you are not a pensioner,with limited means,who was scare mongered into parting with six grand,for utterly bogus work...)
Priceless. :) :)
That is bad..... I got quoted £3k for a replacement boiler on a rental by BG when they phoned me up and I told them I had someone doing it for £1400 all I go was an, oh!
What is a "gas engineer" doing poking around an electrical installation when he is there just to service the boiler? Not being qualified (at his own admission) to make sound judgement on the state of the installation, if he had some concerns then he should have recommended that an electrician was to take a look.
There is such a big fuss about anybody touching a boiler other than a "gas engineer" yet they are free to poke about doing tests on the electrics they possibly don't understand!
Sarah, take the advice of the good folk who have posted thus far and don't get scare mongered into anything. It is good practice to get the electrical installation checked out if you have any concerns. But for peace of mind, hire the services of an experienced professional who knows what they are doing.
A couple of years ago I was doing some work in a property when Mr BG turned up to service the boiler ... the "engineer" spent more time trying to persuade the customer to get a new fuseboard (she had a 16th type) than he did updating her on the state of the boiler......
After he left I asked what she thought about his "electrics" sales pitch - "ignore it" was her reply!
Why would you get BG to do anything in your house, be it gas or electric??
It would be a bit like asking Michael Jackson to babysit your kids....
(Branching out ,Power flushes ,New boiler , rewires ,what next ?)
Maybe they will go into therapy. If you are feeling down you can go to them for a chat... See how many people they will section....
Oh my,they will have cornered the market
They got the Boiler bit
They frighten that customer with nonsense electric scaremongering :eek:
The customer gets anxiety issues worried about fires and imminent death:(
The BG therapeutic department takes over to guide them through their troubles :cool:
Just need a decent credit % to trap you......
once was called out to a house where same thing occored. BG fitter 's socket and see said EFLI >100 ohms. My MFT said 352 ohms. however.... Ze at up front RCD was 0.2 ohms. on outgoing terminals of RCD it was 349 ohms !!!. with the RCD linked out Zs came down to 0.75 ohms. i recommended a board upgrade but customer was about to spend 15K on a kitchen and said he could not afford. Bullsh!t.
it's all down to image. he can show off his new kitchen to whoever, but a new CU is of little interest to their neighbours. a bit like Joan Collins spending £40K on her latest facelift and not putting out £300 for a belly tuck.
£15k on a kitchen, you should have advised the client to try harder at work and to get promoted as then they could afford a better kitchen and your fee.
How much is a board upgrade?
Depends on several things Is main bonding in place, test results, some circuits may not pass muster, how many ways circuit breaker are required, could be wrong, depends on the area £400/£500. You will need to get a quote from an approved Electrician, read the guide I attached, could also be you don't need a board change.
  • Best-Practice-Guide-1-Issue-3-(4).pdf
Reply to Question - British Gas engineer says there is a fault ? in the Central Heating Systems area at ElectriciansForums.net
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
This is quite lengthy so get comfy... I had a bizarre call out relating to a job I attended about five years ago. The situation was they were...
Hi all, New to the forum! Quick background on me: I have a degree in electrical engineering and spent many years working with qualified...
7K
