My RCD began to trip several months ago. I narrowed it down to a fridge/freezer in the garage. However, after turning this off, its now started to trip again due to another fridge/freezer (in the last few weeks). Either I’m incredibly unlucky and both appliances need replacing, or there’s something more sinister causing it to trip. Not sure whether to buy new ones or whether the RCD unit or something else is to blame?
Sounds like you are just incredibly unlucky, if after unplugging the second fridge/freezer the tripping problem has been resolved.
You could get the appliances and RCD tested but my feeling is it will just confirm what you already know.
It could be a N-E fault, and it is triggered by the compressor kicking in. So any large load would do the same as it causes enough of a volt drop on the neutral so sufficient current is diverted via the earth/CPC for the RCD to notice, and the fault may not be on the circuit you think is causing it if the RCD is also feeding a few other circuits.
If you have anything else with a large-ish motor that starts directly, say an old vacuum cleaner (not one with a soft-start electronic control) you could see if that does the same thing at that socket.
An electrician could run an IR test for such a fault, also they ought to be able to check for obvious faults on the appliance (the "PAT testing" sort of check). They also can test the RCD trip times and ramp-test to see what leakage current it actually trips at.
Replacing things "just in case" can be a more frustrating and expensive approach than methodical testing!
This! Totally unrelated N-E fault is much more likely than two similarly faulty fridge freezers.
What other circuits are fed by this RCD?
In most situations like this it's less that 2 hours work for a decent sparks to identify what is going on. That would be considerably less than replacing the appliance again.
You said "after turning this off". To ask a silly question, is it still plugged into the wall with the switch off?
Typically happened most in the middle of the night (so was easier to assume freezer compressor), but on other occasions it’s just been quite random (definitely not when using another large compliance).
Yes, plug in but switched off. Does that make a difference?
The RCD covers mainly an area that was part of an extension the previous owners did to create a utility room. So sockets, some lights, outside lights, immersion. On the sockets we have the washing machine, dryer, x2 fridge/freezers (utility and in garage). Most of the time it happened at night. I’ve attached photo of fuse box / RCD.
So does the RCD trip every night with the fridge freezer switched on,
What make / model is the fridge freezer
No, it’s been inconsistent. Went through a period where it was tripping randomly, then when it got cold happened more frequently until we unplugged the first appliance and then unplugged the second when it started to trip again (which is why it seemed odd). Brands are indesit and maytag.
St Neots
United Kingdom
RCD keeps Tripping, need some Advice
Benjohnson20,
Benjohnson20,