Ok apologies, manowarcs. Just read his thread properly. But I would recommend doing IR test for neutral-earth fault, and check to make sure all appliances etc are disconnected before doing RCD test.
 
Last edited:
I did that once whilst scratching round in an understands cupboard with a dying head torch and not enough light to realise I'd plugged them on the wrong way round

Think what you mean is that you once heard someone else had done than and you are just relaying the info ....

Is your tester set for the correct RCD type?

Ive also heard that this can happen if you're testing with the wrong RCD setting!
 
The test button on the RCD functions just fine, I think I ruled out it being a problem with the RCD. There's clearly a problem with the wiring somewhere, I suppose I was more curious about what sort of problem would cause the RCD to behave in that way. I'd have thought any sort of earth fault would make it impossible to set in the first place...no? It is a TN-C-S system though, so I'll go back and look at that again.

I didn't do a global insulation resistance test, I did each circuit separately. Some of the wiring is old, so I was expecting a problem. Was pleasantly surprised not to get one, but that's also part of what's baffled me now.

No problems with my tester settings, I quadruple check that sort of thing any time I get unexpected results.

Thanks to everyone that's taken the time to reply though.
 