When testing RCD's at the board, its a good idea to switch off all the MCB's
Discuss RCD not tripping under test in the UK Electrical Forum area at ElectriciansForums.net
I've only just wizzed through this thread, so apologies if this has already been mentioned. Are you a DIY'er? What tests have you done on your circuits? Have you done a global insulation resistance test? A neutral to earth fault can cause an RCD not to function, especialy in a TN-C-S supply. Does the test button on the RCD function?
I did that once whilst scratching round in an understands cupboard with a dying head torch and not enough light to realise I'd plugged them on the wrong way round
Is your tester set for the correct RCD type?