Discuss RCD Testing at CU in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

C

chrisgc

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:  American Electrical Advice Forum

Hi

Whats the method for testing RCD's at the consumer unit (as opposed to plug/socket method).

I have a Metrel MI3000 Easi Plus tester which is either 2 or 3 lead tester.
 
Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members

Amp David

-
Mentor
Arms
Green lead on earth bar and red lead on the line terminal of the load side of RCD, press button and waits for it to finish the tests.

Thats how its done on a Megger 1552 anyhow.
 
E

Engineer54

  • Thread Starter Thread Starter
  • #4
Green lead on earth bar and red lead on the line terminal of the load side of RCD, press button and waits for it to finish the tests.

Thats how its done on a Megger 1552 anyhow.
Do you not disconnect the load side before testing??
 

Reply to RCD Testing at CU in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Aico Carbon Monoxide Detectors
This official sponsor may provide discounts for members
SuperlecDirect - ElectriciansForums.net Electrical Suppliers
This official sponsor may provide discounts for members
Top Bottom