Whats the method for testing RCD's at the consumer unit (as opposed to plug/socket method).

I have a Metrel MI3000 Easi Plus tester which is either 2 or 3 lead tester.
 
Aico 3000 Range
This official sponsor may provide discounts for members

Amp David

-
Mentor
Arms
Green lead on earth bar and red lead on the line terminal of the load side of RCD, press button and waits for it to finish the tests.

Thats how its done on a Megger 1552 anyhow.
 
^^^^^^^^^^^^^^^^^ and the fluke and Martindale as well

Don't the new all dancing meggars do it 2 lead though?
 
E

Engineer54

  • Thread Starter Thread Starter
  • #4
Green lead on earth bar and red lead on the line terminal of the load side of RCD, press button and waits for it to finish the tests.

Thats how its done on a Megger 1552 anyhow.
Do you not disconnect the load side before testing??
 

Amp David

-
Mentor
Arms
As above!!
 
Easier and quicker to do at board
 