Try disconnecting the neutral next time mate and taking the 'bulb' out or your dad will 'lamp' you :)

- - - Updated - - -



I knew what you meant mate:)

the bulb was out the light was disconnected and the natural was disconnected
 
Did you disconnect the junction box under the floorboards? :)

Or should that be 'under the laminates' lmao
 
rewire as in re wire, replace a run of cable between light fittings and switch cus of ir fault

Before you rip up floor boards, why don't you use your R2 lead and confirm that this "isolated" cable, is in fact, isolated completely from the CU
 
I think you are going to cause unnecessary work here. Post up your test results the IR readings! If its showing 0.00 Meg switch to ohms and see what it is reading and I bet its a low figure due to it back feeding into the neutral via the line and back to earth at your CU. If the RCD is tripping surely that is telling you something so sort that connection issue out first. Just out of interest what was the reason you started doing the tests :90: As Murdoch has said get your wander lead out for starters !
 
Only winding you up Allan, I always call them bulbs mate the above comment is what I get off of the lads at the wholesalers when I constantly ask for bulbs.
 
Only winding you up Allan, I always call them bulbs mate the above comment is what I get off of the lads at the wholesalers when I constantly ask for bulbs.

Don't worry mate I'm not easily wound up and i knew :)
 
We used to get a cuff round the back of the head too. A bulb is the glass that encases a 'filament', the 'whole thing is called a filament lamp'.
 
We used to get a cuff round the back of the head too. A bulb is the glass that encases a 'filament', the 'whole thing is called a filament lamp'.


Yeah rite I give in mate...............

Next time I go to my supplier I need to ask for a 60 watt filament lamp or a 100 watt lamp ?

He'll then say...............eh!!!
stop talking shiiiiite and tell me what bulbs you want fgs:)
 