RCD tripping on circuits after new board change nitemare

Discuss RCD tripping on circuits after new board change nitemare in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Always do eicr on installation before you change board slow down do the tests properly once there ok you can change board in few hours it's easy knowing in advance your board is not going to trip learnt the hard way myself when I was younger lol
 
Testing before or afterwards dont suppose really matters does it, its still a fault

A better thing when quoting would be to inform the client of the price and then notify them that you have a hourly charge for finding faults on on completion of the new board

Ironically i changed a board this morning, never tested before hand and powered it up, from experience i had already pre determined that they maybe a borrowed neutral from landing light, and there certainly was, so lighting circuits went onto the same mcb, not conventional maybe but not really breaking any rules
 
Testing before or afterwards dont suppose really matters does it, its still a fault

A better thing when quoting would be to inform the client of the price and then notify them that you have a hourly charge for finding faults on on completion of the new board

Ironically i changed a board this morning, never tested before hand and powered it up, from experience i had already pre determined that they maybe a borrowed neutral from landing light, and there certainly was, so lighting circuits went onto the same mcb, not conventional maybe but not really breaking any rules
The only rule it is breaking is that a potentially dangerous situation exists for any electrician working on the circuits who assumes that the wiring was done correctly in the first place.
Seen an electrician thrown off steps due to a borrowed neutral.
 
Well whats he doing working live then?

The lighting circuits are on the same MCB, so if anyone needs to work on this circuit they should be isolating

I could understand your point if i had put them on seperate mcbs on the same side
 
even then, you isolate the circuit, then before anything else, check (at the fitting or whatever you are working on) for dead.
 
Still a wiring which was not carried out correctly due to ignorance of the original installer.
You cannot condone borrowed neutrals left on an installation.
 
Nobody said they condoned it, but if the client doesnt want damage or cannot afford to have the circuit altered the alternative is putting them onto the same mcb, yes not conventional but practical and still safely protected by mcb and rcd. Do you understand that if someone isolates that mcb that the neutral wont be live?
 
the problem could arise if you had too many lights on the 2 circuits for the 6A MCB. fair enough if wired in 1.5mm, you could uprate the MCB to 10A ( subject to no serious derating issues ), but if circuits are in 1.0mm, then you'd be in the fertilizer
 
Definatley Tel, but elaborated too much on the original theory

The idea of couple the two circuits into one mcb isnt dangerous, unless like you say about derating etc... But then you could argue an "electrician" would know this
 
Please tell me Mick what was obvious?

Ill tell you whats obvious and if you are an electrician shame on you as its basic stuff

If i couple them two circuits into one mcb and isolate it means no power is going out which means nothing is coming back on the neutral, thats what made me laugh, as its simple theory, if you cant grasp that you shouldnt be working on equipment or trying to tell an electrician that its "potentially dangerous" as the next electrician could get a belt
 
Hi I agree, but sometimes you get an old 4 way BS3036 board with NO extra play on cables with CPC & neutrals twisted together and to carry out these test with old board in is virtually impossible.

T&E

Never understood why after a cu change people start having problems due to existing faults, if you aren't prepared to address them then should you really be changing the board in the first place?
 
Regardless of anything, if you can't trace and fix faults then your in the wrong job.

Sharing an mcb as stated removes the borrowed neutral as it becomes a single circuit, prefer not to see it done this way but sometimes it's the only option
 
Its no good clutching at straws.
It is because of things like this that we test the way we do.

Do all the tests, and in the correct order, you will then know if you have a problem with the fixed wiring, and you will be able to identify the reason for the RCD trip, especially if you have a very low IR result, or some interconnection with your circuit.

I will assume that as you have done this job, you are registered or have notified if not, and so you are competent to Inspect and Test, so i dont need to go in depth with these testing procedures, it is all in your GN3 anyway.

Cheers.............Howard
 
Vernal what would happen if you didn't test before hand and fitted new board and the ir tests were that poor due to old cables that they wouldn't take rcd board rewire would be needed better to no condition of installation before hand
 

Reply to RCD tripping on circuits after new board change nitemare in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock