Hi all,

On a ground floor ring main protected by a 30amp bs3036 rewirable fuse the owner has reported the 100ma rcd trips out on any occasion where her bathroom extractor fan is on at the fused spur and she tries to use the Hoover.

After looking at her bathroom extractor fan, I've seen that it's being supplied off the ring main via a fused spur with a 13amp fuse and switched from the lighting circuit. So it has live and neutral from the FCU in 2.5mm then a live 1.5mm connected from a ceiling rose connected to the lighting circuit. Two earths are connected in a choc box inside the fan casing and the 1.5mm neutral is not connected.

She says that it doesn't trip if the FCU is in the closed position, it only trips in the open position with the Hoover.

Any ideas what could be causing this?
 
A bit lost with the details.

If the FCU is closed it does not trip but trips when the fan is on! Then you say it trips when the FCU is in the open position. !

The RCD is detecting 50mA or more of leakage so I think the test equipment needs to come out and further info is required.

The fan set up needs sorting with the borrowed neutral from another circuit.

Is the RCD protecting the entire installation or just the ring ! I would imagine its the entire!

Have any tests been carried out ?
 
sort the fan out first. then, with all items disconnectred, IR test and RCD test.
 
A bit lost with the details.

If the FCU is closed it does not trip but trips when the fan is on! Then you say it trips when the FCU is in the open position. !

Oops my fault, the FCU is in the closed (on) position when the RCD that protects the entire TT installation trips.

It has no effect on the power if it's in the open (off) position.

telectrix said:
Sort the fan out first

Probably best that it go on the lighting circuit, with a 3 pole fan isolator and 30ma rcd.

But in the mean time I guess I need to inspect the wiring a little closer.
 
Have you check what type of fcu ie single pole or double if old then its a single pole so the earth and neutral is not broken I had a problem like this until I realised that a fixed electric fire was fed from a sp fcu and it had a neutral to earth fault
 
It turned out to be a neutral to earth fault caused by a nail that had be driven through the skirting board into the cable and stayed put for 26 years tripping the elcb everytime the circuit was overloaded.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Minnions
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other

Thread Information

Title
RCD tripping
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
12
Unsolved
--

Advert

Thread statistics

Created
rustynails,
Last reply from
GLENNSPARK,
Replies
12
Views
4,497

Advert

Back
Top