Hi all,

On a ground floor ring main protected by a 30amp bs3036 rewirable fuse the owner has reported the 100ma rcd trips out on any occasion where her bathroom extractor fan is on at the fused spur and she tries to use the Hoover.

After looking at her bathroom extractor fan, I've seen that it's being supplied off the ring main via a fused spur with a 13amp fuse and switched from the lighting circuit. So it has live and neutral from the FCU in 2.5mm then a live 1.5mm connected from a ceiling rose connected to the lighting circuit. Two earths are connected in a choc box inside the fan casing and the 1.5mm neutral is not connected.

She says that it doesn't trip if the FCU is in the closed position, it only trips in the open position with the Hoover.

Any ideas what could be causing this?
 
A bit lost with the details.

If the FCU is closed it does not trip but trips when the fan is on! Then you say it trips when the FCU is in the open position. !

The RCD is detecting 50mA or more of leakage so I think the test equipment needs to come out and further info is required.

The fan set up needs sorting with the borrowed neutral from another circuit.

Is the RCD protecting the entire installation or just the ring ! I would imagine its the entire!

Have any tests been carried out ?
 
sort the fan out first. then, with all items disconnectred, IR test and RCD test.
 
A bit lost with the details.

If the FCU is closed it does not trip but trips when the fan is on! Then you say it trips when the FCU is in the open position. !

Oops my fault, the FCU is in the closed (on) position when the RCD that protects the entire TT installation trips.

It has no effect on the power if it's in the open (off) position.

telectrix said:
Sort the fan out first

Probably best that it go on the lighting circuit, with a 3 pole fan isolator and 30ma rcd.

But in the mean time I guess I need to inspect the wiring a little closer.
 
If the Rcd protects the whole installation, I'd say if it's only when the double pole fcu is turned on it must be either the cabling from here to the fan, or the fan. N-E I'd guess.
 
Have you check what type of fcu ie single pole or double if old then its a single pole so the earth and neutral is not broken I had a problem like this until I realised that a fixed electric fire was fed from a sp fcu and it had a neutral to earth fault
 
It turned out to be a neutral to earth fault caused by a nail that had be driven through the skirting board into the cable and stayed put for 26 years tripping the elcb everytime the circuit was overloaded.
 

Reply to RCD tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
320
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock