Nate39

Hello all
This is the biggest forum I'm aware off.

We had an electrician carryout an EICR, there were several C2 faults noted, mainly because the consumer unit has no RCD protection and is old, apart from this everything else seemed ok. A unsatisfactory report was issued. He had said that in order to issue a satisfactory EICR these works will need doing. Which ive just had done, and the electrician has issued a satisfactory EICR rather than an EIC - now i will go back and ask him, but before i do and dont want to look silly.

Is this correct to issue an EICR rather than EIC? - because i understood this is notifiable and seems it wouldn't be if an EICR is issued rather than EIC

Thanks
 
If the consumer unit has been upgraded then yes an EIC should have been issued and a part P notification either posted or emailed to you! Depending on what the C2 issues were they may have been covered by minor works certification.
 
Also, there is no requirement to have a 2nd EICR saying "Satisfactory", evidence the work is completed is sufficient.
As above, that particular work should have resulted in an EIC, and is notifiable work.
 
If the consumer unit has been upgraded then yes an EIC should have been issued and a part P notification either posted or emailed to you! Depending on what the C2 issues were they may have been covered by minor works certification.
Thanks, so why eould
Also, there is no requirement to have a 2nd EICR saying "Satisfactory", evidence the work is completed is sufficient.
As above, that particular work should have resulted in an EIC, and is notifiable work.
Thanks, thats what i thought. i did check and he is registered with the NICEIC
what would be the purpose in doing it this way, is there a purpose, and now im worried i wont get a completion notice for a new installation of the consumer unit
 
I'm pleased to learn he is a CPS scheme member - I was expecting the reason this has happened would turn out to be that he wasn't.
I can't offer a logical reason other than work avoidance why this would have happened, it's less work to delete the C2's and send you the EICR again.

You now need to follow the NICEIC complaints procedure and step one is to contact him again (in writing by post, email or text) saying it's your understanding that this is notifiable work and should have resulted in an EIC and part P notification.
If he refuses then you can follow this procedure:
 
Just to add to Tim's post, how long ago was the work completed? We have 28 days to submit jobs to our CPS. Have you tried asking him for the registration number of your job. When I register a job I will send the notification number on the email with the certification I have issued!
Sy
 
If there is a dispute with paying I can tell
you this, the said spark can notify the work, but he does not need to hand over the test certs until being paid. And that comes from the Niceic.
 
Just to add to Tim's post, how long ago was the work completed? We have 28 days to submit jobs to our CPS. Have you tried asking him for the registration number of your job. When I register a job I will send the notification number on the email with the certification I have issued!
Sy
I tried calling him, I'll try again later
Think its better to just ask him to clarify
 
If there is a dispute with paying I can tell
you this, the said spark can notify the work, but he does not need to hand over the test certs until being paid. And that comes from the Niceic.
I dont issue certs until payment is made; the NAPIT notification software/portal for notification asks for an email for the customer so they can send the notification direct. i really dont like this set up as it gives unscrupulous types chance to take the P tbh.
 
I dont issue certs until payment is made; the NAPIT notification software/portal for notification asks for an email for the customer so they can send the notification direct. i really dont like this set up as it gives unscrupulous types chance to take the P tbh.
I've not tried it but would it work to just turn off "Use Electronic Delivery" and put your own details in for the certificate despatch address...
1631910597014.png
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Recent EICR
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
13

Thread Tags

Advert

Thread statistics

Created
Nate39,
Last reply from
timhoward,
Replies
13
Views
2,923

Advert

Back
Top