Hi Guys,

Recently I had an issue with a ring main in my flat either the circuit was over loaded or the connection at the breaker was poor. Either way it ended up with a burnt out breaker with black scorch marks on the top and melted cables by the breaker. As the flat is rented i'm unfortunately not allowed to change anything with out prior approval from letting agency.

Where i'm going with this is i'm pretty new to the whole trade and don't want to question the electrician they sent to fix it but i'm concerned that he has oversized the breaker. He's replaced the broken 32A with a 40A the ring main is wired with bog standard 2.5mm T+E. I'm pretty sure if i've remembered my teachings right that at most for a ring main it is 32A. Should i be questioning this ?

Ben
 
Thats what i thought it was, But what i'm questioning is the electrician replace the old 32A breaker with 40A for a ring main using 2.5mm cable ?
 
either that, or one of those faulty electrium breakers subject to recall. unusual to fit a 40A though.
 
Thats what i thought it was, But what i'm questioning is the electrician replace the old 32A breaker with 40A for a ring main using 2.5mm cable ?

Oops, sorry mate. yes, get him back as I wouldn't be running a 2.5mm T&E ring on a 40A breaker
 
Yes a 32Amp breaker is the way to go, the guy that fitted the 40amp probably it was all he had or he was to lazy to go and get the proper breaker
 
weird, that, coz. in general we usually have loads of 32A going spare after replacing with 16A or 20A when we do board changes and find 2 radials in a 32A.
 
Reg 433.1.5 specifically lists 30 or 32a protective devices only in the requirements for standard ring circuits,so a 40a device does not comply.
 
Maybe..... Hes coming back, and was concerned the existing MCB was faulty so stuck (an albeit too large) valued new MCB in its place.

i would prefer a new 40A mcb than a clapped out 32A one. Even if its just for a day.

am i bad
 
Maybe..... Hes coming back, and was concerned the existing MCB was faulty so stuck (an albeit too large) valued new MCB in its place.

i would prefer a new 40A mcb than a clapped out 32A one. Even if its just for a day.

am i bad

Shockingly bad.....but yes,nowt wrong with a temp 40a to get things going. Much wrong with an RCD replaced with a main switch to stop it tripping as I saw recently,and he charged the bloke £400 quid to do that.
 
P.s. At least they replaced the RCD with something. - Ive seen the RCD butchered open and bodged with a bit of cable INSIDE the rcd then taped back together.....
 
Whilst on the subject of RFC breaker sizes, I went to a job the other week because the lady said the MCB kept tripping when several appliances were on...

it it was a ring as I tested it, in 2.5/1.5, well that's what it appeared to be in the CU, had end to end continuity etc.

the circuit was protected by a 16A breaker though.

as it happens she didn't ask me back as the landlord got someone in, but what are your thoughts on changing a breaker for a bigger one as I was tempted to swap it for a 32A but then thought, why is it a 16A, am I missing the obvious? MYbe the person who fitted it did it for a reason.

whats your thoughts on upping it?
 
if you#re sure it was a RFC with e-e continuity, then fitting a 32A would be fine. a possibility though is that there could be several unfused spurs off the RFC and a previous spark downrated the MCB to allow for the spur loading.
 
That's my thinking, I guess without pulling every faceplate off and going back to basics you will never know 100%.

its one if those things where I would rather take a miss on it just incase, for what it's worth it's bit always worth the potential hassle.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Ring Main Breaker Size
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
18

Advert

Thread statistics

Created
benlwatts,
Last reply from
egg67,
Replies
18
Views
18,337

Advert

Back
Top