Hi, looking for suggestions or indeed what you guys do when wiring in SWA to plastic house CUs.

gland swa to a Metal JB then connect from JB to CU?

Fit sub main like the wylex fused isolator using 25mm meter tails via henley blocks to keep supply out of house CU rcds?

fit gland plate/nut to plastic CU then.fit glanded cable to this then earth gland plate to cu earth bar? Use breaker on rcd side?

its a 30 meter run 10mm 3core SWA spare 40 and 45 amp breaker available in CU.

Just looking for ideas of what you guys do, cheers
 
Your details say "DIY" but in Scotland, so the Part P building requirements don't apply. The forum rules don't allow for advice that might be dangerous/illegal to follow, but you seem to be asking sane questions. Can you clarify your electrical skill/experience?

In terms of the actual question, it kind of depends on the use of the summer house and how much trouble power loss would cause. If you have a spare 40A MCB slot then it is easy to feed a small CU and feed sockets, lights, etc, but you will have poor selectivity between MCB/MCB(RCBO) due to both having the "instant" magnetic trip.

With SWA you could feed it via a fused-switch, sized as high as the SWA fault-clearing Zs will allow to get good selectivity, but ideally also 1.6 times smaller then the DNO fuse to ensure total selectivity with that. For example, if you have a 63A DNO fuse then a sub-main on 63/1.6 = 40A (closest) fuse cannot blow your DNO fuse no matter what.

But doing so means splitting your house CU tails, and that means you either have an isolator already or will need the DNO to pull the fuse to allow the work to take place.

For the SWA gland it can go in to plastic, but you need to use the banjo or an "Earthing nut" to properly bond the armour to the MET to allow fault clearing, even if 3 core so it has the CPC inside.

Unless you have some real experience in doing this I would say you should get in a professional. You see what the details are, discuss your options, and if acceptable do the cable install (or duct, so you can also run network cable along side it, etc) yourself.
 
Your details say "DIY" but in Scotland, so the Part P building requirements don't apply.
No, but it's common sense to do things properly and safely - Scottish volts are as dangerous as English ones.

The forum rules don't allow for advice that might be dangerous/illegal to follow, but you seem to be asking sane questions.
My first thought was that he's asking questions which aren't related either/ors -

gland swa to a Metal JB then connect from JB to CU?

Fit sub main like the wylex fused isolator using 25mm meter tails via henley blocks to keep supply out of house CU rcds?
Are not two different ways to "wire SWA to plastic house CUs".


Can you clarify your electrical skill/experience?
Good question - I'm concerned that he's picked up a few terms here and there but doesn't truly understand them. Can't help thinking that anybody really competent to do this work would know whether he wanted the summer house fed from the CU or not.

Then there's the T-word....


Unless you have some real experience in doing this I would say you should get in a professional. You see what the details are, discuss your options, and if acceptable do the cable install (or duct, so you can also run network cable along side it, etc) yourself.
plus_one.gif
 
Hi, thanks for the feed back.

Yes I come from an electrical back ground, mainly industrial, oil rigs/platforms. Mainly maintenance on LV/HVelectrical systems, power generation and instrumentation
Have done plenty of SWA glanding into motors,switchboards and various other apperatus etc.
Perhaps I did not word my original post in a coherant way. I do apologise for that, I did not expect to criticised for seeking information.

PC1966 has answered my question and I am going for the banjo. I just wanted to be 100% that this was fine to do.I thank you for that.

I will of course be more down with the lingo if I have further questions, after all this is what forums are for or atleast what I though they were for.

Have a nice day :)
 
I should add that if glanding to plastic you are much better to use an Earthing nut / piranha nut (instead of traditional banjo) as they lock to the threads and retain a good contact / no loosening without too high a compressive force for the plastic. These sort of things:

Just need a ring crimp terminal for the fixing screw to wire transition. Personally I would connect both ends (armour to CPC core/earth terminal) even if you would be OK for fault clearing on the armour alone (i.e. R1 + R2 of armour is enough to meet Zs when attached just at the source, not needing parallel CPC to bring down Rs at the load end), just gives that extra path for safety.
 
Last edited:
I should add that if glanding to plastic you are much better to use an Earthing nut / piranha nut (instead of traditional banjo) as they lock to the threads and retain a good contact / no loosening without too high a compressive force for the plastic. These sort of things:

Just need a ring crimp terminal for the fixing screw to wire transition. Personally I would connect both ends (armour to CPC core/earth terminal) even if you would be OK for fault clearing on the armour alone (i.e. R1 + R2 of armour is enough to meet Zs when attached just at the source, not needing parallel CPC to bring down Rs at the load end), just gives that extra path for safety.
Thanks for your advice PC 1966 it is appreciated

All the best ?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Scotland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Summer house
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8
Unsolved
--

Advert

Thread statistics

Created
farqu01,
Last reply from
Soi disant,
Replies
8
Views
1,882

Advert

Back
Top