Woaaaaaaa! Really one last thing, I've uploaded a pic of van cu, here's why.
Was busy minding my own business happily glanding the new feed, and decided to check out the board with a temp supply with correct polarity into existing ex caravan site blue flex,well the neutral bar is live, the way it would have been on site. It's got a tested by sticker and number on it, I'll maybe save that for later.
Never worked with these Hager units, but looks like rccb is wired wrong.
I've checked for terminal markings and diagram, but none,and not much out in Internet land, it's a cd240u.
The way it's wired is
Topleft. L in
Top right. N in
B left. N to busbar
B right. L busbar link to mcbs.
I guess there are a couple of ways of rectifying, looking for some pointers if anyone has experience of these french unit s please.
As I say, polarity of temp supply is true.
View attachment 35586