During an EICR I havr encountered swa feeding 1 lamppost not glanded at the post end, the feed is connected to the chassis of the 3 phase DB.

I was thinking this would attract a C3 code, but I thought I post it and ask others what they think?

It's fed from a 6 amp type a hagar rcbo tho it was fed from a mcb till I changed it.
Screenshot_20230217_165132_Gallery.jpg
 

Attachments

  • Screenshot_20230217_165120_Gallery.jpg
    107 KB · Views: 13
C3 for lack of gland and it should be supported somehow.

I guess the lamp post is the enclosure… needs tool to open.
Ones ive fitted in the past had a brass plate at the bottom of the fuse cut out for glanding.

There’s a cpc core, so the armour only needs earthed at one end, but there should be something at post end of the cable.
 
There is no earth to the cutout either, therefore no earth to the lantern. Does this particular fitting not require an earth or has it just been ignored?
 
There is no earth to the cutout either, therefore no earth to the lantern. Does this particular fitting not require an earth or has it just been ignored?
There is one cable in the earth block that is unaccounted for.... maybe it goes all the way up to the lantern head?
 
The door doesn't need an earth but there should be a secondary barrier to enclose conductors and live parts. Problem with those cut outs is they have no facility to connect an SWA cable.
 

Reply to Swa outer connected both ends in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
696
For various reasons out of my control, we have wound up in a situation where we have 1.5mm SWA cables buried in these pillars and exiting out of...
Replies
95
Views
7K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
405
Hi guys, So, a friend of mine has a three phase 100a supply and wants to install 2 x three phase 20a fork lift chargers and a three phase car...
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock