During an EICR I havr encountered swa feeding 1 lamppost not glanded at the post end, the feed is connected to the chassis of the 3 phase DB.

I was thinking this would attract a C3 code, but I thought I post it and ask others what they think?

It's fed from a 6 amp type a hagar rcbo tho it was fed from a mcb till I changed it.
Screenshot_20230217_165132_Gallery.jpg
 

Attachments

  • Screenshot_20230217_165120_Gallery.jpg
    Screenshot_20230217_165120_Gallery.jpg
    107 KB · Views: 13
C3 for lack of gland and it should be supported somehow.

I guess the lamp post is the enclosure… needs tool to open.
Ones ive fitted in the past had a brass plate at the bottom of the fuse cut out for glanding.

There’s a cpc core, so the armour only needs earthed at one end, but there should be something at post end of the cable.
 
There is no earth to the cutout either, therefore no earth to the lantern. Does this particular fitting not require an earth or has it just been ignored?
 
There is no earth to the cutout either, therefore no earth to the lantern. Does this particular fitting not require an earth or has it just been ignored?
There is one cable in the earth block that is unaccounted for.... maybe it goes all the way up to the lantern head?
 
The door doesn't need an earth but there should be a secondary barrier to enclose conductors and live parts. Problem with those cut outs is they have no facility to connect an SWA cable.
 
The door doesn't need an earth but there should be a secondary barrier to enclose conductors and live parts. Problem with those cut outs is they have no facility to connect an SWA cable.

Just googled the part number and it seems the base is plastic with a couple of grommets supplied.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

newfutile

Arms
Supporter
-
Joined
Location
hemel hempstead
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Swa outer connected both ends
Prefix
N/A
Forum
Electrical Testing & PAT Testing Forum
Start date
Last reply date
Replies
9

Thread Tags

Advert

Thread statistics

Created
newfutile,
Last reply from
SparkySy,
Replies
9
Views
1,347

Advert

Back
Top