Hi guys,

how would you code a SWA cable which feeds a DB within a commercial unit with no seperate CPC so only realying on the SWA strands as means of CPC

If it is only a CPC then it is almost certainly compliant (unless your testing suggests otherwise) with current regulations.

If it is also required to perform the function of a main bond then you will need to do further calculations and consider other variables to confirm that it is ok.
 
Hi guys,

how would you code a SWA cable which feeds a DB within a commercial unit with no seperate CPC so only realying on the SWA strands as means of CPC


What size is the SWA is it 2 core 3 core or what, seem to recall that up to and including 95mm 2 core is the limit for using the steel as the cpc, I have a table somewhere giving details, but to busy at the mo to look for it, I got it from Google a while back try (pvc xlpe)
 
Last edited:
What size is the SWA is it 2 core 3 core or what, seem to recall that up to and including 95mm 2 core is the limit for using the steel as the cpc, I have a table somewhere giving details, but to busy at the mo to look for it, I got it from Google a while back try (pvc xlpe)

Be wary of the tables floating around the Internet, they aren't exactly correct, more of a rough guide.
Calculation is the only real way of proving it
 
I personally dont like relying on the SWA although regs are quite happy about it. Always scared SWA comes loose on gland.
Are other forum members comfortable with only the SWA ?
Wouldn't your concerns be applicable to any earthing application, they are only as good as the method and means in which they are terminated and the competence of the person doing the termination, SWA glands are perfectly fine for the job, its down to the installer to ensure the glands (s)he fits do actually fit the cable correctly and are tight, and where required, an earth tail fitted to the earthing lug or bar.
 
This question smacks of someone carrying out periodic inspection and testing without the knowledge and experience to be doing so. It's amazing how often people comdemn situations which are fully compliant with BS 7671.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
North

Thread Information

Title
SWA seperate CPC
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
paulthemagpie,
Last reply from
davesparks,
Replies
15
Views
2,629

Advert

Back
Top