Hi there, Three phase board, 125A isolator, are tails 25mm ok? Shouldn't the neutral be bigger?
Im having EDF monday, and i need to be sure.


Thank you
 
No meter jet, this is new build, 3 x 100A fuses, 3 ph fuse box, tnc-s system.
EDF comming monday to install the meter.
 
Ok mate i see what your saying 25mm ok for all meters if you have 3 x 100a ! only time it changes is if you have 300a fuses then its 35mm so 100a-to-CT is 35mm unless like some factories they might install a small sub-station outside (400A) and run 50mm tails but you have 3 x 100A so 25mm fine and Neutral is still 25mm.
Regards
Kung.
 
Last edited by a moderator:
Neutral would be same size as your tails, and if you have 100A x3 incoming board fuses 25mm is ok mate.
 