I have been asked to finish a job to connect a 1.5mm SWA cable into a DB which feeds a post to power some security cameras.

The SWA cable enters the building and into some metal trunking. The trunking butts up to the DB and there is a large entry hole into the DB through which the existing cables go. See picture.

How is it best to terminate the SWA? Is it best to bring the cable out of the trunking through a PVC gland and then terminate into the DB using the usual SWA terminating gland on the DB? Is there a better solution?

Obviously it would look better if I didn't need to bring the cable out of the trunking and back into the DB..
 

Attachments

  • Image DBs.jpg
    Image DBs.jpg
    135.2 KB · Views: 171
an alternative might be, at the load end of the circuit, where the swa enters the trunking.
gland it off there and just run the singles or inner multicore down the trunking.
 
The Radius of the cable will be quite large, as well as rge gland, can't see that working very well especially in a small size of trunking, no not a good idea in my thinking, still all are entitled to their own opinion.
True, pal. Depends on the trunking size and space and, in truth, it's better to be on site seeing the true situation before making a decision. It's all conjecture and we're only offering ideas to the lad. We'll see how he goes about it, hopefully.
[automerge]1580335426[/automerge]
an alternative might be, at the load end of the circuit, where the swa enters the trunking.
gland it off there and just run the singles or inner multicore down the trunking.
Good idea. If it's not too far or difficult access. Adapt box on trunking for terms maybe.
 
Last edited:
it depends on what is connected, most of the time it is easier to put an isolator there just to terminate the swa into.
£15 for an isolator of that size, its not worth messing about with. load to isolator in swa, isolator close coupled or conduit to trunking. all done, looks neat, bill paid!!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Kent

Thread Information

Title
Terminating SWA into DB
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
18
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
MajorPileup,
Last reply from
ipf,
Replies
18
Views
6,775

Advert

Back
Top