Can we as electricians pick up on a broken PEN conductor?

I’ve installed an EV charger for FIL, and everything tested fine, but there is a fault condition on the charge point itself.
Turns out the fault condition is their PEN detection.
At the moment, the charge point isn’t doing anything. (No car delivered yet)

Is there a test I can do to prove it, or just contact supplier?
 
Can we as electricians pick up on a broken PEN conductor?

I’ve installed an EV charger for FIL, and everything tested fine, but there is a fault condition on the charge point itself.
Turns out the fault condition is their PEN detection.
At the moment, the charge point isn’t doing anything. (No car delivered yet)

Is there a test I can do to prove it, or just contact supplier?
Do Ze a the CU, see what reading you have. How did you found it's a PEN fault?
 
Do Ze a the CU, see what reading you have. How did you found it's a PEN fault?
I’ll recheck Ze… don’t have the paperwork with me just now.

The manufacturer help desk told me what the fault was in respect to the colour of the LEDs on the charge point itself.
 
Do you know how it detects a broken PEN? To me the sort of thing I would look for are:
  • A significant voltage between CPC and true Earth, say above around 15V or so (needs a rod)
  • Mains voltage out of range (how some open PEN boxes work I believe)
  • High current in bonding conductors
The supply voltage could be down to other causes, but is bad news, while the former is a real indication of a problem. I took 15V as about 13% drop on the DNO side equally on L and PEN, just as a guess.

Edited to add check bonding conductor(s) for high currents with a clamp meter, you might have no other signs of a fault but something is very wrong and hidden by some pipework doing the job it was never intended to do. especially a gas meter!
 
Last edited:
I’ll recheck Ze… don’t have the paperwork with me just now.
If you mean test it again - I actually wouldn't in this scenario.
In a suspected broken PEN scenario, disconnecting the main earth conductor is the last thing you want to be doing.

The video below goes into more detail.
As @pc1966 said the two factors most chargepoint's use are the voltage range being outside 207-253v. The video also points out that a lot of PV installs in the area and and being close to the transformer can result in false positives as the perceived supply voltage can be high enough to trigger it.

 
Last edited:
I popped by today, but no one was in. Couldn't get into the house
Took a reading from a garage socket... just to double check and got a voltage of 248v. Zs on that socket of 0.48... which will be close to the Ze.

Reading some of the other comments on the facebook group, they suggested logging off the app, and going back in seems to solve a lot of issues... and guess what... it did!
 
Reading some of the other comments on the facebook group, they suggested logging off the app, and going back in seems to solve a lot of issues... and guess what... it did!
I hope that solved it.
If anything like down here, it was nice and sunny yesterday and very overcast today, so potentially the perceived supply voltage could have been higher yesterday if there are a few PV installations locally. 248v is close to the 253v upper limit after all.
 
I hope that solved it.
If anything like down here, it was nice and sunny yesterday and very overcast today, so potentially the perceived supply voltage could have been higher yesterday if there are a few PV installations locally. 248v is close to the 253v upper limit after all.
That’ll be 248 with his PV feeding back. It’ll be lower at night.
 

Reply to Testing for broken PEN in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Would any fellow electricians consider using an open PEN device to protect a metal trailer used as a "Canteen". It is likely to be often connected...
Replies
3
Views
280
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used...
Replies
44
Views
7K
Hi all, I've installed a Tesla Gen 3 wall charger supplied by my client. For your information, the place that I installed is in a block of flat...
Replies
2
Views
1K
I am an NICEIC contractor but I have never installed an Electric vehicle charger. I have watched all of the relevant NICEIC webinars (The wire) on...
Replies
18
Views
952

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock