Just wondering how to go about testing continity on a lollipop circuit, radial to ring. But no access to junction box (not my fault), obviosly there are only one set of twin earth at the breaker, which was 40amp and I downgraded it to a 32amp because I didn't think it was safe to have the 40 who ever did this must of not thought about it.

It's 2.5 ring
6mm radial
 
IR test as normal. get your Zs readings at sockets, record highest. the downsizing to 32A is correct, as you need to fit OCPD to heve a lower In than the Iz of the smallest cable/s, so that's the 2.5mm "ring" on the circuit. make note in comments.
 
Seem to remember reading somewhere, that the individual circuits, radial part & RFC part should be tested separately and the results recorded separately on a cert'; which because of the nature of recording the test results would have to be an EIC. That is, the R1+R2 values for the radial and loop values for the RFC?

PS, which is going to be difficult if you can't access the JB.
 
Last edited:
Seem to remember reading somewhere, that the individual circuits, radial part & RFC part should be tested separately and the results recorded separately on a cert'; which because of the nature of recording the test results would have to be an EIC. That is, the R1+R2 values for the radial and loop values for the RFC?

PS, which is going to be difficult if you can't access the JB.

You would not need to do that, it would not acheive anything other than burning time. Although not standard practice, at the end of the day, It is still one circuit and should just be recorded as such. The Zs recorded would just be the highest value at a socket as usual. Note on minor works that there is a 6mm2 cable jointed to 2.5mm ring final and that junction is inaccessible.
 
i woul say an end to end test at the back of one socket outlet is essential here, otherwise there could well be 32A radial on 2.5mm t&e. I would also add i agree with you downgrading from 40-32 mcb is a good move but you shouldnt have done before confirming the ring otherwise it could need a 20A mcb
 
You would not need to do that, it would not acheive anything other than burning time. Although not standard practice, at the end of the day, It is still one circuit and should just be recorded as such. The Zs recorded would just be the highest value at a socket as usual. Note on minor works that there is a 6mm2 cable jointed to 2.5mm ring final and that junction is inaccessible.
Not sure your right, but then again neither am I.

This is what I'm thinking; It is not just one circuit, it's a hyrbrid circuit. Certainly the RFC part of the circuit would be need to be tested insequence as normal, to establish if it is installed and connected correctly. This can be achived without access to where the circuits join, if the radial circuit is isolated at the supply. But there is no method of accurately confirming the measurement of the radial cpc R1+R2 or R2, without access to the joint?
Hence the reason for the testing & recording the two circuits separately.
 
Last edited:
You would not need to do that, it would not acheive anything other than burning time. Although not standard practice, at the end of the day, It is still one circuit and should just be recorded as such. The Zs recorded would just be the highest value at a socket as usual. Note on minor works that there is a 6mm2 cable jointed to 2.5mm ring final and that junction is inaccessible.


TJ not sure where the Minor works certificate come into play on this post,
 
Not sure your right, but then again neither am I.

This is what I'm thinking; It is not just one circuit, it's a hyrbrid circuit. Certainly the RFC part of the circuit would be need to be tested insequence as normal, to establish if it is installed and connected correctly. This can be achived without access to where the circuits join, if the radial circuit is isolated at the supply. But there is no method of accurately confirming the measurement of the radial cpc R1+R2 or R2, without access to the joint?
Hence the reason for the testing & recording the two circuits separately.

I do see where you are coming from and I am not saying I am right either. The way I see it though is it is just another termination on the same circuit and the ring can still be proved from end to end testing at a socket outlet. We still still modify other circuits where we know they must have junctions but we can't access them and we just go on our test results which all we can reasonably do sometimes.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Uk
Business Name
DBelec

Thread Information

Title
Testing lollipop circuit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
38
Unsolved
--

Advert

Thread statistics

Created
Dan Brown,
Last reply from
westward10,
Replies
38
Views
9,612

Advert

Back
Top