Hi Miketwinny

Your original question was how you would class this supply.
Well moving on, that supply cable looks very much like a jute covered, steel and lead covered cable
which would indicate it was intended as a TNS supply. It would be the largest TNCS supply cable i have ever
seen and also the 1st where the N/E was not taken from the service head. This very much looks
like the earth is a sweated joint onto the steel/ lead. As I said on my original post all your asking is for
the supply authority to confirm type of supply.
Just trying to put in some helpful info mate.
 
Jeysuz I can't hardly believe what I'm seeing. - someones driven an earth rod in but an inch from the service mains and the gas mains......

thats more of a worry!

Don't think there is any concern.

If you look closely there is a fresh concrete pour where the services are coming up.
I think you will find the rod was placed in the vertical service trench prior to the concrete being poured.
You would have quite a job driving a copper rod through solid concrete.


TN-S (once proven) and leave it at that.
 
Last edited by a moderator:
Did you test the Ze? What was the TNS Ze?

im just wondering now why on earth that rod is there



This was common practice in the 50's on council estates. Absolutely nothing wrong in it either. Though from the photo, this looks like one of those thin twigs, and if it is, it hasn't been in for 43 years!! They didn't make thin twigs in those day's, they were all 10 foot X 5/8''-3/4'' proper rods in them days!! lol!!
 
Re: TN-S & TT on same installation what should I class it as?

ballpark figure? £750 - £1500? assume to replace cable & labour etc.
I'd figure much more, my local DNO charge 750 just for cutting a service and terminating in new meter box, and we did the digging, fitted the box and supplied the hockey stick.
7 vans = 7 men times 2 hours and I bet they are close to 750 before the add on any call out or digger or materials

- - - Updated - - -

ballpark figure? £750 - £1500? assume to replace cable & labour etc.
I'd figure much more, my local DNO charge 750 just for cutting a service and terminating in new meter box, and we did the digging, fitted the box and supplied the hockey stick.
7 vans = 7 men times 2 hours and I bet they are close to 750 before the add on any call out or digger or materials
 
Don't think there is any concern.

If you look closely there is a fresh concrete pour where the services are coming up.
I think you will find the rod was placed in the vertical service trench prior to the concrete being poured.
You would have quite a job driving a copper rod through solid concrete.


TN-S (once proven) and leave it at that.


Who knows!

And yes you are right, driving a rod through concrete would be difficult.
 
Maybe at some point in the past (or from new) the Ze simply wasn't good enough so to lower it or there was a 'long time to fix' fault they knocked a rod in. If it's been concreted/screeded in like that from new suggests to me it got put in when you could see what was going on underneath.
Done a Ze test today 0.16ohm well below the max 0.8ohm for a TN-S system so disconnected the earth rod from the MET and will leave rod alone as now redundent and class as TN-S on EIC.:smiley2:
 
Done a Ze test today 0.16ohm well below the max 0.8ohm for a TN-S system so disconnected the earth rod from the MET and will leave rod alone as now redundent and class as TN-S on EIC.:smiley2:

Why disconnect the rod, what harm do you think it's doing?? It was always a TN-S, even before you disconnected the rod!!

The fact is, you now have an extraneous earth, in close proximity to both gas and electrical supply that isn't now connected to the MET!! A bit foolish don't you think?? lol!!
 
Why disconnect the rod, what harm do you think it's doing?? It was always a TN-S, even before you disconnected the rod!!

The fact is, you now have an extraneous earth, in close proximity to both gas and electrical supply that isn't now connected to the MET!! A bit foolish don't you think?? lol!!
True, live and learn.What would you recommend grind rod down and fill hole or just connect to MET with new clamp and 10mm cable.
 
Just connect this rod up as it was before, (maybe cut a bit off the top if you want) with as you say a new clamp and 10mm cable. A bit too close to the gas pipe to be playing around with a grinder in my opinion.... lol!!
 
All sorted new clamps on Gas & Rod and new MET earth.jpg
 
True, live and learn.What would you recommend grind rod down and fill hole or just connect to MET with new clamp and 10mm cable.

Gotta hold my hand up Mike and admit I missed that too until it was pointed out so your not alone lol.
Bloody easy this game innit:thinking:
 
Re: TN-S & TT on same installation what should I class it as?

What's the story with the copper pipe top-side of the earth clamp? Is that some sort of horrendous bending job? Daz

- - - Updated - - -

What's the story with the copper pipe top-side of the earth clamp? Is that some sort of horrendous bending job? Daz
 