True, live and learn.What would you recommend grind rod down and fill hole or just connect to MET with new clamp and 10mm cable.

Gotta hold my hand up Mike and admit I missed that too until it was pointed out so your not alone lol.
Bloody easy this game innit:thinking:
 
Re: TN-S & TT on same installation what should I class it as?

What's the story with the copper pipe top-side of the earth clamp? Is that some sort of horrendous bending job? Daz

- - - Updated - - -

What's the story with the copper pipe top-side of the earth clamp? Is that some sort of horrendous bending job? Daz
 
It is simply a TN-s system period as you have a suppliers earth as your primary earth. The Earth rod is purely that and is not and should not be translated as a TT system. The earth rod is there as a belt and braces job and to provide and give a better earth path only. The only issue you may have is a PFC as with the very low resitance to earth you will possibly get a very high Earth Fault current exceeding the Ka of your protective device/devices. Your short circuit fault current will be considerably lower. In Compex installation the better the earthing arrangement - and in design additional earth rods are by design placed in the installation for greater protection. Why remove it as its offering a good additional earth path - doing its job.
 
I doubt he will have any higher than 3-4Ka maximum, even if he's near the Dno tx.
Yep aggree as however PFC could be as high and should not 16Ka on a 230 supply as per OSG page 70 As said May be high so a measure to ensure devices meet capasity
 
Considering the pefc being circa 1.4ka I doubt it's higher than 2ka.

Your right that it should be tested, and I'm sure the op has done.
 
It is simply a TN-s system period as you have a suppliers earth as your primary earth. The Earth rod is purely that and is not and should not be translated as a TT system. The earth rod is there as a belt and braces job and to provide and give a better earth path only. The only issue you may have is a PFC as with the very low resitance to earth you will possibly get a very high Earth Fault current exceeding the Ka of your protective device/devices. Your short circuit fault current will be considerably lower. In Compex installation the better the earthing arrangement - and in design additional earth rods are by design placed in the installation for greater protection. Why remove it as its offering a good additional earth path - doing its job.

I doubt very much, if that thin twig is going to offer any form of addition protection to this TN-S installation whatsoever!! lol!!

Higher earth fault current, exceeding KA of protective devices?? Only in your wildest of dreams!! lol!!
 
I'd be getting that gas pipe and cooker installation checked out. Pipe looks like it's been hammered to &!**@#. Daz
 
Its just a TNS system with supplementary rod I imagine, not uncommon.
Don't disconnect the rod as suggested by someone earlier in thread though - As you when then have an Unbonded exteraneous conductiive part.
Leave it alone, I would possibly note the stake in the bonding section.
 

Reply to TN-S & TT on same installation what should I class it as? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
758

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock