Discuss TN-S & TT on same installation what should I class it as? in the UK Electrical Forum area at ElectriciansForums.net
M
Miketwinny
got a 16mm earthing conductor from main supply sheath goin in to the MET + an earth electrode(rod) next to the supply with a 10mm earthing conductor comin off it to the MET
Should I class it as a TT system for test results and mark the EIC as TN-S & TT :nonod: earth.jpg
Jeysuz I can't hardly believe what I'm seeing. - someones driven an earth rod in but an inch from the service mains and the gas mains......
thats more of a worry!
seen a few like that. and don't worry about the services, he's only driven the rod in half way;LOL.
theres every chance its a dno bodge , seen dafter things done by power companies.
either way , tn-s is by far the better earth path and should be given precedence over tt.
Maybe at some point in the past (or from new) the Ze simply wasn't good enough so to lower it or there was a 'long time to fix' fault they knocked a rod in. If it's been concreted/screeded in like that from new suggests to me it got put in when you could see what was going on underneath.
My advice is not to make any judgement call on this one. Call in your local supply authority to address this HORROR show
or u could get egg on your face, they can confirm TNS max 0.8 ohms or TNCS max 0.35 ohms for your Ze's
They are normally very helpful and it should be free of charge
Let us all know the outcome
Should I class it as a TT system for test results and mark the EIC as TN-S & TT :nonod: View attachment 17960[/QUOTE
**** me...If this is the way he creates a earth then I think it would be safer without... Close or What
My advice is not to make any judgement call on this one. Call in your local supply authority...They are normally very helpful and it should be free of charge
:D From what I've read on here if you phone them up and mention an earth stake they think you are talking about an eco-friendly slab of beef.
Tell you what Tigi, you must be very lucky and have gotten through to the one person at the local DNO who actually knows what you're talking about and how to help you. Every time I've done it round here I get the image of that Little Britain character...Computer says naw
It's takes brave or stupid man to knock a rod in so close to the incoming services!!
On the subject of the earthing. I would first verify that there was a good TNS earth of less than 0.8ohms. If so, then run a new 16 mm earth up to the CCU from the MET and do away with the TT earth altogether as it is not needed.
You think that was close !!!
One of our lads had a wee mishap this morning while installing a stake on a local farm .
It was a 3ph 35mm incomer before he literally blew it clean apart on all 3 phases , the supply side was still live when they got to us !
I knew it was going to be painful when the first two vans turned up but my arse near on gave out when the other three turned up !!!!!!!!!!!!:disappointed::disappointed::disappointed::disappointed::disappointed:
View attachment 18005View attachment 18006View attachment 18007View attachment 18008View attachment 18009
That was bad luck!
Now the question we are all wanting to ask - who pays??
so you would just go with this would you....rather than get a measured value eh?
LOL....
That was bad luck!
I have already assumed the position and await delivery of the bill while firmly gripping my ankles , with out even a hint of any Vaseline in sight !!!!:blush2:
What do you reckon it will be then ?
A builder we work with hit two only a few months apart last year on a local estate we work for , i think the first was £7000+vat and second was £5500+vat !:dunce2: But in fairness they were both HV underground and not LV like this one .
been like that from new 43 years no problems guna do a Ze test soon.
Surely you had a wee peak at that Tx between the shed and the pole? Would yer man not have figured that the cable didn't dissipate through the atmosphere and that it was most likely underground? lol.
It was actually some form of voltage suppressor and not a Tx apparently but that is besides the point , just thought i would throw that in as even the jointer's had not seen one before !
I'm afraid you just can't call it until the bill arrives. On an optimistic note there have been a couple of instances recently where my DNO have charged nothing ?? One was a serious moving of the incoming power so that the client could have the incoming service moved. Cable excavated with mini digger, cut, jointed and extended. All FOC - was Very impressed.
Fingers crossed then:):)
Hi Miketwinny
Your original question was how you would class this supply.
Well moving on, that supply cable looks very much like a jute covered, steel and lead covered cable
which would indicate it was intended as a TNS supply. It would be the largest TNCS supply cable i have ever
seen and also the 1st where the N/E was not taken from the service head. This very much looks
like the earth is a sweated joint onto the steel/ lead. As I said on my original post all your asking is for
the supply authority to confirm type of supply.
Just trying to put in some helpful info mate.
Don't think there is any concern.
If you look closely there is a fresh concrete pour where the services are coming up.
I think you will find the rod was placed in the vertical service trench prior to the concrete being poured.
You would have quite a job driving a copper rod through solid concrete.
TN-S (once proven) and leave it at that.
Did you test the Ze? What was the TNS Ze?
im just wondering now why on earth that rod is there
This was common practice in the 50's on council estates. Absolutely nothing wrong in it either. Though from the photo, this looks like one of those thin twigs, and if it is, it hasn't been in for 43 years!! They didn't make thin twigs in those day's, they were all 10 foot X 5/8''-3/4'' proper rods in them days!! lol!!
Re: TN-S & TT on same installation what should I class it as?
ballpark figure? £750 - £1500? assume to replace cable & labour etc.
I'd figure much more, my local DNO charge 750 just for cutting a service and terminating in new meter box, and we did the digging, fitted the box and supplied the hockey stick.
7 vans = 7 men times 2 hours and I bet they are close to 750 before the add on any call out or digger or materials
- - - Updated - - -
Who knows!
And yes you are right, driving a rod through concrete would be difficult.
Done a Ze test today 0.16ohm well below the max 0.8ohm for a TN-S system so disconnected the earth rod from the MET and will leave rod alone as now redundent and class as TN-S on EIC.:smiley2:
Why disconnect the rod, what harm do you think it's doing?? It was always a TN-S, even before you disconnected the rod!!
The fact is, you now have an extraneous earth, in close proximity to both gas and electrical supply that isn't now connected to the MET!! A bit foolish don't you think?? lol!!
True, live and learn.What would you recommend grind rod down and fill hole or just connect to MET with new clamp and 10mm cable.
Just connect this rod up as it was before, (maybe cut a bit off the top if you want) with as you say a new clamp and 10mm cable. A bit too close to the gas pipe to be playing around with a grinder in my opinion.... lol!!
Gotta hold my hand up Mike and admit I missed that too until it was pointed out so your not alone lol.
Bloody easy this game innit:thinking:
What's the story with the copper pipe top-side of the earth clamp? Is that some sort of horrendous bending job? Daz
- - - Updated - - -
It is simply a TN-s system period as you have a suppliers earth as your primary earth. The Earth rod is purely that and is not and should not be translated as a TT system. The earth rod is there as a belt and braces job and to provide and give a better earth path only. The only issue you may have is a PFC as with the very low resitance to earth you will possibly get a very high Earth Fault current exceeding the Ka of your protective device/devices. Your short circuit fault current will be considerably lower. In Compex installation the better the earthing arrangement - and in design additional earth rods are by design placed in the installation for greater protection. Why remove it as its offering a good additional earth path - doing its job.
I doubt he will have any higher than 3-4Ka maximum, even if he's near the Dno tx.
Yep aggree as however PFC could be as high and should not 16Ka on a 230 supply as per OSG page 70 As said May be high so a measure to ensure devices meet capasity
Reply to TN-S & TT on same installation what should I class it as? in the UK Electrical Forum area at ElectriciansForums.net
Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...