M

Miketwinny

got a 16mm earthing conductor from main supply sheath goin in to the MET + an earth electrode(rod) next to the supply with a 10mm earthing conductor comin off it to the MET
Should I class it as a TT system for test results and mark the EIC as TN-S & TT :nonod: earth.jpg
 
Maybe at some point in the past (or from new) the Ze simply wasn't good enough so to lower it or there was a 'long time to fix' fault they knocked a rod in. If it's been concreted/screeded in like that from new suggests to me it got put in when you could see what was going on underneath.
 
My advice is not to make any judgement call on this one. Call in your local supply authority to address this HORROR show
or u could get egg on your face, they can confirm TNS max 0.8 ohms or TNCS max 0.35 ohms for your Ze's
They are normally very helpful and it should be free of charge
Let us all know the outcome
 
got a 16mm earthing conductor from main supply sheath goin in to the MET + an earth electrode(rod) next to the supply with a 10mm earthing conductor comin off it to the MET
Should I class it as a TT system for test results and mark the EIC as TN-S & TT :nonod: View attachment 17960[/QUOTE

**** me...If this is the way he creates a earth then I think it would be safer without... Close or What
 
Tell you what Tigi, you must be very lucky and have gotten through to the one person at the local DNO who actually knows what you're talking about and how to help you. Every time I've done it round here I get the image of that Little Britain character...Computer says naw
 
It's takes brave or stupid man to knock a rod in so close to the incoming services!!

On the subject of the earthing. I would first verify that there was a good TNS earth of less than 0.8ohms. If so, then run a new 16 mm earth up to the CCU from the MET and do away with the TT earth altogether as it is not needed.
 
Last edited by a moderator:
got a 16mm earthing conductor from main supply sheath goin in to the MET + an earth electrode(rod) next to the supply with a 10mm earthing conductor comin off it to the MET
Should I class it as a TT system for test results and mark the EIC as TN-S & TT :nonod: View attachment 17960[/QUOTE

**** me...If this is the way he creates a earth then I think it would be safer without... Close or What

You think that was close !!!
One of our lads had a wee mishap this morning while installing a stake on a local farm .
It was a 3ph 35mm incomer before he literally blew it clean apart on all 3 phases , the supply side was still live when they got to us !
I knew it was going to be painful when the first two vans turned up but my arse near on gave out when the other three turned up !!!!!!!!!!!!:disappointed::disappointed::disappointed::disappointed::disappointed:


155.jpg159.jpg167.jpg170.jpg163.jpg
 
You think that was close !!!
One of our lads had a wee mishap this morning while installing a stake on a local farm .
It was a 3ph 35mm incomer before he literally blew it clean apart on all 3 phases , the supply side was still live when they got to us !
I knew it was going to be painful when the first two vans turned up but my arse near on gave out when the other three turned up !!!!!!!!!!!!:disappointed::disappointed::disappointed::disappointed::disappointed:


View attachment 18005View attachment 18006View attachment 18007View attachment 18008View attachment 18009

That was bad luck!

Now the question we are all wanting to ask - who pays??
 
My advice is not to make any judgement call on this one. Call in your local supply authority to address this HORROR show
or u could get egg on your face, they can confirm TNS max 0.8 ohms or TNCS max 0.35 ohms for your Ze's
They are normally very helpful and it should be free of charge
Let us all know the outcome
so you would just go with this would you....rather than get a measured value eh?
LOL....
 
That was bad luck!

Now the question we are all wanting to ask - who pays??

I have already assumed the position and await delivery of the bill while firmly gripping my ankles , with out even a hint of any Vaseline in sight !!!!:blush2:

What do you reckon it will be then ?

A builder we work with hit two only a few months apart last year on a local estate we work for , i think the first was £7000+vat and second was £5500+vat !:dunce2: But in fairness they were both HV underground and not LV like this one .
 
got a 16mm earthing conductor from main supply sheath goin in to the MET + an earth electrode(rod) next to the supply with a 10mm earthing conductor comin off it to the MET
Should I class it as a TT system for test results and mark the EIC as TN-S & TT :nonod: View attachment 17960[/QUOTE

**** me...If this is the way he creates a earth then I think it would be safer without... Close or What
been like that from new 43 years no problems guna do a Ze test soon.
 
Surely you had a wee peak at that Tx between the shed and the pole? Would yer man not have figured that the cable didn't dissipate through the atmosphere and that it was most likely underground? lol.

It was actually some form of voltage suppressor and not a Tx apparently but that is besides the point , just thought i would throw that in as even the jointer's had not seen one before !
 
I have already assumed the position and await delivery of the bill while firmly gripping my ankles , with out even a hint of any Vaseline in sight !!!!:blush2:

What do you reckon it will be then ?

A builder we work with hit two only a few months apart last year on a local estate we work for , i think the first was £7000+vat and second was £5500+vat !:dunce2: But in fairness they were both HV underground and not LV like this one .

I'm afraid you just can't call it until the bill arrives. On an optimistic note there have been a couple of instances recently where my DNO have charged nothing ?? One was a serious moving of the incoming power so that the client could have the incoming service moved. Cable excavated with mini digger, cut, jointed and extended. All FOC - was Very impressed.

Fingers crossed then:):)
 

Reply to TN-S & TT on same installation what should I class it as? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock