Hi, i'm trying to identify the rating of a distributors fuse. I have attached a picture of the said fuse. The markings on it state Schneider Type YN6 but give no indication of rating or short circuit capacity. It's been suggested that these are 400A. Anybody come across them?
 

Attachments

  • IMAG0040[1].jpg
    93.7 KB · Views: 79
Hey.

I have seen them before but only in DNO service heads, The fuse is inside the white holder with the black wingnuts on it.

They are usually BS 1361 200A - 400A, 33KA.

No real way of telling without pulling one.

Cheers
 
Agree with Lenny also you might have fuses at the back the front sometimes are covers and you pull these and think the cutout fuses are now removed but looking right at back behind link holders whala there they lye ! their sometimes very small be carefull ! some dont look like fuses just small black links.
Regards
Kung
 
Hi, had an opportunity to take a look at these.

I had the sense to remove all load past the head in case removing the covers actually took the fuses out, and it did, the casings with handles are enclosures with BS88's inside.

Anybody care to comment on the earthing arrangement from my posted picture? Looking at it the neutral comes from the cable armour going to a cutout at the top right of the board. Then an earth wire disappears back underground. My thoughts would be TN-C-S. I just found it interesting with the armour used for N and this additional earth wire.
 
Hi.

I agree it is a TN-C-S, the stranded outer conductor isn't really an armouring as you would find in an SWA as it's usually copper and is intended to be a conductor.

I have seen the board do this many times where they install a seperate earth back out and bury it in their trench, thus backing up the PME with a TT, also helping to keep the neutral at or near earth potential as they do all the way back to the transformer.

Cheers
 

Reply to Trying to identify distributors fuse in the Australia area at ElectriciansForums.net

Similar Threads

A recent EICR turned up a fault: an RCD fused spur was feeding a socket and a shower pump, and neither socket or pump had continuity on the CPC...
Replies
17
Views
3K
Hey there! I am fitting four lights in my kitchen and have come across two issues (pictures attached - this is really the best quality I could do...
Replies
4
Views
2K
Just interested in peoples thinking on using the neutral through the earthing system like I came across today. I've come across many wrong...
Replies
10
Views
2K
Over the holiday period my partner returned home to her apartment with no power. None of the internal breakers in the consumer unit had tripped...
Replies
24
Views
3K
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock