Evening all,

Went round to a clients house and did some tests on an outdoor socket. At the junction (in an IP rated wiska box) between the cable coming in from the house and the SWA running to a single outdoor double socket down the garden, the IR test between L-E fails at 0.05 Mohms. When the ends of both cables are disconnected from each other, and the IR tests are done on each cable separately (L-N, L-E, N-E), everything passes! It's only when I test between the earth coming from the house and the line of the SWA that I get the 0.05Mohms. The SWA is being supplied by an FCU inside the house off of a kitchen ring. Supply is TN-C-S.

Any advise much appreciated!

Red
 
Evening all,

Went round to a clients house and did some tests on an outdoor socket. At the junction (in an IP rated wiska box) between the cable coming in from the house and the SWA running to a single outdoor double socket down the garden, the IR test between L-E fails at 0.05 Mohms. When the ends of both cables are disconnected from each other, and the IR tests are done on each cable separately (L-N, L-E, N-E), everything passes! It's only when I test between the earth coming from the house and the line of the SWA that I get the 0.05Mohms. The SWA is being supplied by an FCU inside the house off of a kitchen ring. Supply is TN-C-S.

Any advise much appreciated!

Red
The fault is not between L and the CPC then, it is between L and true earth. Is the armour of the SWA connected to the CPC at either end?
 
This is now solved. Armour of SWA wasn't connected to CPC on either end, and upon further testing found that there was continuity between L and armour of SWA. Turns out L and SWA armour were acting as a path to earth, hence the reading between L of swa and cpc of cable from the house. Turns out @Pretty Mouth was right. Thanks for the help.
Well done. Out of interest, how/where was L touching armour?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Birmingham, WEST MIDLANDS, uk
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Very strange IR fault - any one seen this before?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
Redline8400,
Last reply from
DPG,
Replies
6
Views
2,526

Advert

Back
Top