K

Keith the beef

Can anyone tell me is the allowable volt drop for a three phase supply to a sub main 3%?????

Cable length 120m
100A supply
Correction factor .81 per ampere per meter

100Ax120mx.81
1000 = 9.72v


400x3%=12v

so this is good ya?


Keith
 
BRB pp 287

50mm 4c

resistive 0.86

120*100*0.86/1000 = 10320/1000 = 10.32v

any good ??

400* 5% = 20v
 
Last edited by a moderator:
ok, i got my .81 off table 4D4B
As table 4D4A opposite shows CCC for ref method D buried in ground.

Am i correct in this????

Thanks Keith
 
remmeber the maximum volt drop permitied is from origin of installation. What its best to do is to keep the volt drop of the sub mains to a maximum of 1% so the rest can go on the final circuits.
3% lighting
5% power
Also dont use the protective device size use the design current it gives a tru volt drop.
hope this helps.
 
i have this bloody armoured that is in situ and am trying to work out what fuse ratings it should be backed up with, i've found out from the manufacturer it's a 50mm 4 core, they have used the swa as earth the csa of the steel braiding is 85mm. i believe this translate to approx a 10mm cpc copper conductor, am struggling with adiabatic equation trying to work what fuses can safely be put in front of this cable, currently has 100A bs 88's

Can anyone guide me on this for a 3 phase supply?
 
Minimum Size of Earth = K1 x S
K22

K1 = 115 K2 = 51 S = 50

115/51 = 2.255
50/2 = 25
2.255 x 25 = 56mm well under your 86mm

What rating is the sub main as that would be the Ib the fuses are for

Don’t for get the K value in the adiabatic will be 51
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Volt drop on three phase sub main
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
Keith the beef,
Last reply from
john.irvine,
Replies
9
Views
7,578

Advert