K

Keith the beef

Can anyone tell me is the allowable volt drop for a three phase supply to a sub main 3%?????

Cable length 120m
100A supply
Correction factor .81 per ampere per meter

100Ax120mx.81
1000 = 9.72v


400x3%=12v

so this is good ya?


Keith
 
BRB pp 287

50mm 4c

resistive 0.86

120*100*0.86/1000 = 10320/1000 = 10.32v

any good ??

400* 5% = 20v
 
Last edited by a moderator:
remmeber the maximum volt drop permitied is from origin of installation. What its best to do is to keep the volt drop of the sub mains to a maximum of 1% so the rest can go on the final circuits.
3% lighting
5% power
Also dont use the protective device size use the design current it gives a tru volt drop.
hope this helps.
 
i have this bloody armoured that is in situ and am trying to work out what fuse ratings it should be backed up with, i've found out from the manufacturer it's a 50mm 4 core, they have used the swa as earth the csa of the steel braiding is 85mm. i believe this translate to approx a 10mm cpc copper conductor, am struggling with adiabatic equation trying to work what fuses can safely be put in front of this cable, currently has 100A bs 88's

Can anyone guide me on this for a 3 phase supply?
 
Minimum Size of Earth = K1 x S
K22

K1 = 115 K2 = 51 S = 50

115/51 = 2.255
50/2 = 25
2.255 x 25 = 56mm well under your 86mm

What rating is the sub main as that would be the Ib the fuses are for

Don’t for get the K value in the adiabatic will be 51
 

Reply to Volt drop on three phase sub main in the Electricians' Talk | All Countries area at ElectriciansForums.net

Similar Threads

I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
This is quite lengthy so get comfy... I had a bizarre call out relating to a job I attended about five years ago. The situation was they were...
Replies
11
Views
1K
After my last post and having and having to re-learn some stuff can someone check and advise on a few things. Sorry if this is wrong don't hate...
Replies
7
Views
2K
Hi A good friend of mine is having a large electrical installation carried out in his garden.Hes had 3 prices from various electrical contractors...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock