Discuss Volt drop on three phase sub main in the Electricians' Talk | All Countries area at ElectriciansForums.net
K
Keith the beef
Can anyone tell me is the allowable volt drop for a three phase supply to a sub main 3%?????
Cable length 120m
100A supply
Correction factor .81 per ampere per meter
100Ax120mx.81
1000 = 9.72v
400x3%=12v
so this is good ya?
Keith
BRB pp 287
50mm 4c
resistive 0.86
120*100*0.86/1000 = 10320/1000 = 10.32v
any good ??
400* 5% = 20v
remmeber the maximum volt drop permitied is from origin of installation. What its best to do is to keep the volt drop of the sub mains to a maximum of 1% so the rest can go on the final circuits.
3% lighting
5% power
Also dont use the protective device size use the design current it gives a tru volt drop.
hope this helps.
i have this bloody armoured that is in situ and am trying to work out what fuse ratings it should be backed up with, i've found out from the manufacturer it's a 50mm 4 core, they have used the swa as earth the csa of the steel braiding is 85mm. i believe this translate to approx a 10mm cpc copper conductor, am struggling with adiabatic equation trying to work what fuses can safely be put in front of this cable, currently has 100A bs 88's
Can anyone guide me on this for a 3 phase supply?
Minimum Size of Earth = K1 x S
K22
K1 = 115 K2 = 51 S = 50
115/51 = 2.255
50/2 = 25
2.255 x 25 = 56mm well under your 86mm
What rating is the sub main as that would be the Ib the fuses are for
Don’t for get the K value in the adiabatic will be 51
Reply to Volt drop on three phase sub main in the Electricians' Talk | All Countries area at ElectriciansForums.net
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
After my last post and having and having to re-learn some stuff can someone check and advise on a few things. Sorry if this is wrong don't hate...
Hi A good friend of mine is having a large electrical installation carried out in his garden.Hes had 3 prices from various electrical contractors...
Hi folks, I'm installing a 3-ph 32A 60309 socket and just wanted to double check my design calcs are right... The circuit will be part of a 3-ph...
Hi all, new to here. Just designing a sub main, very long time since I have done this so just wanted some thoughts. Its to a summerhouse sort of...
6K