Hi,

I was calculating volt drop today using xlpe armoured cable, 3 core, single phase. Table 4E4A pg 373. I am using 3 core cable but on single phase, so i would assume column 3 for single phase. I was told by the tech helpline although the cable is being used for single phase that column 4 should still be used as it is the number of cores that is the factor. Can anyone tell me why?

Cheers
 
Theoretical the third core can affect the current carrying capacity of the other two cores as it restricts heat dissipation which would increase the conductor resistance but I would say it is negligible. There is a case that for Table 4E4A for the current carrying capacity you should use the columns for a three phase supply if you are using a three core cable on single phase, again I would think this is negligible, I suspect this is the reason.
 
Theoretical the third core can affect the current carrying capacity of the other two cores as it restricts heat dissipation which would increase the conductor resistance but I would say it is negligible. There is a case that for Table 4E4A for the current carrying capacity you should use the columns for a three phase supply if you are using a three core cable on single phase, again I would think this is negligible, I suspect this is the reason.
What he said
 
Hi, Thank you for replies. After looking into this further, I have decided that the tech line was incorrect. The column that should be used, is column 3 for single phase. The third conductor will only carry current under fault conditions, therefore having no bearing on volt drop.

Cheers
 
Hi, Thank you for replies. After looking into this further, I have decided that the tech line was incorrect. The column that should be used, is column 3 for single phase. The third conductor will only carry current under fault conditions, therefore having no bearing on volt drop.

Cheers
I agree with them though the effect of the third core would be debatable.
 
Hi Westward, i spoke to an electrical designer. He told me, if I look in the regs, i'll see that there is no difference in volt drop between between 3 or 4 core cable as it is presumed that 4 core will be supplying 3P & N. The load should be balanced therefore no current flowing in the neutral, 4th core.

Cheers
 
Originally you were using three core for single phase with the third core as a cpc and as such columns for three phase should be used due to the negligible effect of the third core.
As for a three phase circuit being balanced and the neutral carrying no load may work in Utopia but in practice this is highly unlikely. Whether it carrys load or not its presence will affect the other conductors.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

soulman

Arms
-
Joined
Location
Durham

Thread Information

Title
Volt Drop table help
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
soulman,
Last reply from
westward10,
Replies
10
Views
1,805

Advert

Back
Top