Hi guys,
came across a fault yesterday on a job where I was getting 15v between neutral and Earth at two sockets on a ring main.if u need anymore details let me know.
i am unsure what would cause this and want your expert opinion as I have never come across this problem.

the installation is an old 3036 board no RCD
TNS system

your replies are appreciated
 
it could be a phantom voltage. try with an analogue meter. if it's still there, check all earthing and bonding and the cpc connections on the socket circuit.
 
Hi guys,
came across a fault yesterday on a job where I was getting 15v between neutral and Earth at two sockets on a ring main.if u need anymore details let me know.
i am unsure what would cause this and want your expert opinion as I have never come across this problem.

the installation is an old 3036 board no RCD
TNS system

your replies are appreciated

What was the voltage between neutral and earth, measured at the terminals in the board?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Nottingham
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Voltage between Neutral and Earth
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4
Unsolved
--

Advert

Thread statistics

Created
Sb8389,
Last reply from
mojorebel,
Replies
4
Views
2,743

Advert

Back
Top