Hi,
Ive decided to dance with the devil and have signed up with the NIC. I have my inspections comming up and have a couple of questions.
1.Regarding safe isolation, i know the procedure but i dont have a proving unit. Now, when showing my inspector the cu ive changed is it ok to isolate, remove cover, test on meter side of switch, test circuits dead, test on meter side of switch again?
Also, would he fail me for not having locked off the main switch. Ive been trying to get hold of some lockoffs locally, none of my wholesalers have any and say there isnt the call for them!
2.My other nominated job is some extra sockets in a customers kitchen. This work was carried out over 8 weeks ago and now they are part way through having a new kitchen installed. They wont have the splashbacks re-tiled before the inspection so i imagine round the sockets is going to look a bit dog rough. How do i stand on this one? (im going round the day before to check things out).
Cheers for your time.
Ive decided to dance with the devil and have signed up with the NIC. I have my inspections comming up and have a couple of questions.
1.Regarding safe isolation, i know the procedure but i dont have a proving unit. Now, when showing my inspector the cu ive changed is it ok to isolate, remove cover, test on meter side of switch, test circuits dead, test on meter side of switch again?
Also, would he fail me for not having locked off the main switch. Ive been trying to get hold of some lockoffs locally, none of my wholesalers have any and say there isnt the call for them!
2.My other nominated job is some extra sockets in a customers kitchen. This work was carried out over 8 weeks ago and now they are part way through having a new kitchen installed. They wont have the splashbacks re-tiled before the inspection so i imagine round the sockets is going to look a bit dog rough. How do i stand on this one? (im going round the day before to check things out).
Cheers for your time.