I got called out to price up some additional socket outlets for a customer. As I walked around checking things out I could not locate the Main Bonding to the water supply. I pointed it out to the customer, whos reply was "oh I think the kitchen fitters electrician did that, I will ask him". I told them he has bonded the gas, but the water hasn't been done.

Anyway a few days later they send me an email with the minor works certificate attached. Not the first time this has happened, but it does annoy me :mad:

View attachment 35343

View attachment 35344
 
Having done a few kitchen refurbs myself, I've ensured the water service is bonded and has continuity, only to return for 2nd fix to find the kitchen fitters have hidden said bonding behind the floor unit.

Tried educating kitchen fitters no end, seen some that have even hid the water stopcock behind the floor unit. Did bonding accessible behind removable plinth on one job, only to be told off by my scheme assessor, that that was not accessible.

Luckily for me now, I predominately do work for the same kitchen company, where I've educated the fitters. We either have all the pipe work/bonding accessible in floor unit, or drill a large diameter hole in the rear of floor unit where bonding point is easily accessible. :cool:
 
Last one I found with no water bonding was a new installation and the Previous Guy had left that bit of EIC blank. It turned out it was ok but a note on cert would have saved me testing :) .

Maybe there was quick visit from Previous Guy to fix "and btw, since I'm here ..."? Not much fun for you
 
More info needed. Can you see the incoming water service? Are you certain it requires bonding?

Yes I can see it and it does require bonding, there's a hole cut in the rear of the base units to access the stop cock.

Theres only one 10mm2 conductor running from the met to the gas & that's as far as it goes.

The description on the certificate is a bit vague, I always like to put as much useful info as possible so anyone coming in after me has a clear picture.

There's other issues too but that's another thing.
 
Maximum disconnection time permitted 0.2 seconds for TN-C-S earthing arrangement, the RCD type says RCD not A,B,AC etc and says 1.1ohms for maximum Zs permitted by bs7671 when it should be 1.37.....cert looks like tosh.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Gloucestershire

Thread Information

Title
Your opinions please
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7
Unsolved
--

Advert

Thread statistics

Created
Ib≤In≤Iz,
Last reply from
Ib≤In≤Iz,
Replies
7
Views
1,360

Advert

Back
Top