Just tried this method and it still trips the RCBO in the main DBI've always overcome this problem by testing the second RCD using the test probes across its load-side line and supply-side neutral. The tester doesn't care whether the test current returns to earth or neutral, it should still perform a valid test on that RCD provided only the line goes through it. But because the test current returns via the the first RCD's neutral, that sees the tester as a legitimate load and shouldn't trip.