Currently reading:
3 phase supply to classroom, unsure to TT?
Discuss 3 phase supply to classroom, unsure to TT? in the Commercial Electrical Advice area at ElectriciansForums.net
Hi I'm after some advice, ive been asked to connect up a new outbulding at a school, there was a building there before and the 4 core 16mm SWA was already in place. It will be a kind of extra classroom/club room and will have several sockets, lights and a small water heater in the toilet. Heating for the rest of the building isnt decided yet. I plan on fitting a 4 way 3 phase board and running everthing on seperate RCBOs. Probably 2 for lights, 2 for sockets, 1 for water heater and 1 for a fire alarm system. All circuits will obviously be 230v
My question is about the earthing. I thought about exporting the earth (main building TNCS) but im not sure the armour of the cable will be sufficiant. The main cable has also been joined including the armour. There are some main utilitys running under the building so if i TT it i know im going to drive the earth rod in to something! It also means putting a main RCD switch in and this will also mean ill have to try and find a double insulated gland to run the SWA into the board.
Any advice on this would be greatly appreciated.
Why do you think the armour is insufficient. Is it required to support main protective bonding.
Hi - with 16mm 4 core swa it's likely the armour will be sufficient for the CPC of the distribution circuit. But if there are any extraneous conductive parts in the 2nd building then it won't be big enough for protective bonding back to the installation MET in TNCS.
as previous. wtf do you want 3 phase over there ?
Tt is gland swa onto paxolin plate then bolt to base of dB and run earth straight from dB usaly 1 rod will get you around 30-40 ohms
You then have two different earthing systems in close proximity. The gland or end of The cable should be placed within an all insulated enclosure.
That creates a dangerous situation because you have metal connected to two different earthing systems exposed inside the DB.
1 rod? How long, what material, what type of soil, whereabouts in the country, will that be ok for the available fault current?
We do lots of school work and I have yet to see a separate building with a single phase supply.
Do the adebiatic equation to see if the armour is sufficient for cpc, i would also consider using single phase only so you have the spare conductors to export the main earth at the main school.
But 3 phase for the above seems OTT. What would you do? Put 1 phase for the sockets, 1 phase for the lights and 1 phase for the small water heater?
Or is the OP leaving spare phases for the 'heating, which isn't decided yet'?
I would be interested to know.
Maybe a silly question but why 3 phase?
Would single phase not do for what you are intending to install?
Good point I did think that but as the 3 phase supply is there i thought i should ustilise it and i dont know what they are planning on doing heating wise yet. They dont have the budget for heaters at the moment but i can imagine the second its all installed they will want 10x 3kw heaters installing!
Hi , yeah thats the idea to try and balance the loads, i know with things like this in the past they always say they just want a couple of sockets and lights then plans change and if there isnt the option to expand then i will probably get be to blame!
How do i work out the CSA of the SWA though? There is also a join in the cable with an earth strap in place to keep the continuation of the SWA but i'm assuming thats all its good for.
I tested a small what they call a mobile class week before last, consisted of two class areas, WCs and entrance lobby. Twenty two circuits.
Only 22!
You should see the boards in the main part of this school its only a small village school and they have really gone to town on the amount of circuits its mind boggling. Its frustrating because a lot of them arent clearly marked either and there is no paper work from the last periodic.
Reply to 3 phase supply to classroom, unsure to TT? in the Commercial Electrical Advice area at ElectriciansForums.net