I have replaced consumer unit in small rented property, on pre visit found everything fine. Replaced,tested all the circuits, all sound, issued eic.
For letting agency eic is not enough, Eicr is due now, and they wouldn't accepr Eic instead, are they right?
Thanks ;)
Re. Doing an eicr before board change.
Doing it this way in a perfect world would help greatly
I have found that it just really complicates things on the quoting phase and the customer would just get someone else, maybe its the way i explain it though lol
I usually find a reasonably thourough on site survey when quoting is easier for me and if i do get caught out just swallow it
I do allow for it if i think problems might be apparent
However i always undertake
Ze
Ins/res between l-e/n-e
Check positions of gas/water services
Check a good few switchpoints and sockets
Look out for additions and diy add ons
Ive been pretty on the money so far
If it seemed like a diy enthusiast or a few reg flags then i would insist on eicr first but mostly wouldnt
its all ok guys, most of you answers are quite obvious to me, but taking into account landlords rules, are they allowed to keep eic (board change, no comments, installation sound, inspected and tested) in records instead of eicr that is due?
[automerge]1597347298[/automerge]
What is the reason for this now being due ?
eicr due to 5 years period, consumer unit swap due to being plastic, faulty rcd, cracked case and generally client scared of fires..
As stated quite a few times above, you issue an EIC for a board change.
The new letting rules ask for an EICR (every 5 years), which is pretty much the same testing as for a board change, plus some additional inspection.
In this situation (and I'm doing 1 or 2 per week right now) - with the landlord or letting agent agreement - I issue the EIC for the board change, plus an EICR for the new rules - reflecting the installation post board-change. And I add an amount to the invoice to cover the additional work and admin, but it is far more cost effective for them compared to having them done separately.
no, board been changed just now, at the same time as 5 years eicr is due
Well in that case your EIC is for the board not the whole installation. I can see your point that you've tested the circuits but it doesn't certify that you have inspected and tested the rest of the installation. It doesn't mean you shouldn't charge for the EICR.
there is a lot of confusion. with the letting agent i do a lot of work for we have worked out which need eicrs due to not having a valid one, if there is one in place then at a change of tenancy with no changes or alterations etc they will get me to do a visual check. their insurance company have approved this as has the council hmo office
If it was a new build then an EIC would hopefully validate the safety of the installation however, an EIC for a consumer unit change does not encompass the same scope as it is only applicable to the works carried out. If an EICR is due then it should be carried out.
I would undertake the extra work (to obtain any readings not taken during EIC process) issue a cert as required and bill accordingly.
A CU change is just that, it doesn't always do the same in-depth testing as an EICR.