As stated quite a few times above, you issue an EIC for a board change.

The new letting rules ask for an EICR (every 5 years), which is pretty much the same testing as for a board change, plus some additional inspection.

In this situation (and I'm doing 1 or 2 per week right now) - with the landlord or letting agent agreement - I issue the EIC for the board change, plus an EICR for the new rules - reflecting the installation post board-change. And I add an amount to the invoice to cover the additional work and admin, but it is far more cost effective for them compared to having them done separately.
 
no, board been changed just now, at the same time as 5 years eicr is due


Well in that case your EIC is for the board not the whole installation. I can see your point that you've tested the circuits but it doesn't certify that you have inspected and tested the rest of the installation. It doesn't mean you shouldn't charge for the EICR.
 
there is a lot of confusion. with the letting agent i do a lot of work for we have worked out which need eicrs due to not having a valid one, if there is one in place then at a change of tenancy with no changes or alterations etc they will get me to do a visual check. their insurance company have approved this as has the council hmo office
 
If it was a new build then an EIC would hopefully validate the safety of the installation however, an EIC for a consumer unit change does not encompass the same scope as it is only applicable to the works carried out. If an EICR is due then it should be carried out.
 
I would undertake the extra work (to obtain any readings not taken during EIC process) issue a cert as required and bill accordingly.

A CU change is just that, it doesn't always do the same in-depth testing as an EICR.
 

Reply to Eicr requested after consumer unit replacement in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Hi, I am due EICR test on my property which has 20 year old wiring. Last test on 2018 was fine with no issues. Just need to check if my consumer...
Replies
4
Views
1K
Hi, Hoping someone can clarify for me. I've recently moved into a rental property, the landlord had new electric radiators installed and a new...
Replies
3
Views
582
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock