I have run 10mm2 3 core SWA to garage CU but miscalculated the length and no way Im going to reach the house CU. I need to extend the cable, is it acceptable to do it like on the picture?
What about taking the SWA to its own little CU and split the incoming tails with Henley blocks?
House CU can be isolated without affecting garage
Yes that would be acceptable if single insulated cables are going to be exposed then put them in some containment.
A torpedo would probably be the easiest, even if you have to cut the feed cable back so that the join is in the best place.
It would also mean that the Swa can be glanded properly into the CU instead of having to use a junction box.
Thanks of the idea, I will have an electrician replacing my house CU at some point next year, so will definitely consider this option. At the moment I am looking for a temporary solution (as simple and cost effective as possible) and wanted to know if the one I suggested is acceptable and safe
I would definitely go for it but my CU in an old one with the back entry and no slots to gland SWA. I will do it properly when I replace the CU next year. Thank you
Is 10mm² 3 Core HO7RNF suitable to be used instead of single insulated cables in a containment?
Yes that would be ok.
The 6181Y wouldn't have to be in containment as they are double insulated.
I can get 1m of 3 Core HO7RNF and it is a bit tight behind the board so Id rather have one piece of cable and split it only at both ends. Thanks anyway for the advice
You will then need ferrules and a crimper.
Thanks, it worked well, but I have a problem. It turns out that the neutral terminal slots are too small for 10mm2 cable (it's an old CU). Can I run 6mm2 instead of 10mm2 from CU to junction box if I feed it from 30A MCB instead if 40A?
Thank you. I have another problem. It turns out that the neutral terminal slots are too small for 10mm2 cable (it's an old CU). Can I run 6mm2 instead of 10mm2 from CU to junction box if I feed it from 30A MCB instead if 40A?
Yes
essex
Extending SWA garage cable
Luka,
Luka,