brief idea of set-up... bedroom extension atop attached garage. obviously needed planning permission. builder ( or whoever worked for him ) extended house ring final 2 S/O in new bedroom, 3 S/O in garage. wired in 1.5mm 3core with yellow used as cpc. actual cpc connected randomly to back boxes, no continuity or sleeving. ring continuity broken as it was bodge connected in RFC. stand alone RCD fed with a 13A plug top and T/E in plug to feed an outside S/O. how the hell did this pass BC inspection?