gavin26

Hi I need some help with 3 phase wiring. I'm fairly confident I'm right but haven't done it since I was 18. Would I be right in saying that normal 3 phase power for sockets are wired in star and you should end up with 5 cables at each outlet? L1, L2, L3, N & E? With a 3 pole isolator for phases.Also do they have to be wired separately? Or can they be wired as radials?

I've been asked to do some industrial work (which I don't normally do!) what sort of thinks do I look for in regards to sized of cables etc what is the formulas for cable calcs on three phase?

I have a picture of the way I think they are wired but can't upload it because I haven't posted 5 times! Will upload once I can!

Appreciate responses
 
i think from your post you really ought to get someone with 3 phase experience to help you on this job. it's a lot more complex than just wiring up a radial with a few sockets.
 
1 What are the sockets to be used for
2 What load on each socket

Personally I would wire each outlet on seperate radial with a switched / isolated s/o (M.K. Commando range 16a - 125a ) but as Tel say's if your not sure ?
 
I have done 3 phase sockets as an apprentice but never been incharge of the design. I know it's different calcs to single phase etc. probably best getting somebody in with me then!
 
jesus some off you's need to chill out

it's really not that hard but need a few bits of info

what size sockets?
how far is the cable run?
how is the cable installed?
grouped cables how many?
proposed protective devices?
ambient temperature?
 
Hi ranger thanks for response. I know what the guys are saying but would just like a head start. I will in the end hire someone with 3 phase experience.

I couldn't tell you length of runs etc yet but it will more than likely be ran in conduit. Could you tell me the 3 phase formulas
 
we all learnt once!
which is why i suggested he got some expert help with the job. it may be to power motors or other industrial equipment. get it wrong and you're in it up to the neck. apart from that, public liability insurance may not cover him for 3 phase.
 
there is a we bit to observe and i am only learning it so sorry i cant help you as i dont fully understand it cause im a we fish in a big pond but i bark
 
which is why i suggested he got some expert help with the job. it may be to power motors or other industrial equipment. get it wrong and you're in it up to the neck. apart from that, public liability insurance may not cover him for 3 phase.

How many electricians check their insurance before every job to see if they are covered, would seem to be a stupid exclusion for an electrician
 
How many electricians check their insurance before every job to see if they are covered, would seem to be a stupid exclusion for an electrician
it's common. just a way for the insurance companies to screw more out of you.
 
If you were using just one out of the three you’re almost right. Try 400/1.732 instead.

But if you have unbalanced load on each phase interacts with the others giving the 1/3[SUP]rd[/SUP] harmonic current.

For a balanced load (P/3)/(V/√3) = In. but the currents cancel themselves out making the neutral unnecessary. Run a neutral to a star connected motor and it won’t be a happy bunny.
 
Get some decent cable calculation software (cd). It requires the inputs you need most. As with alot of things you don't know. Do your research. Add it up. If all what your powering is 3 phase then n is ok.. So long as your circuit is rated to your breaker then you should be ok..
As I said do your research, and if its safe it is safe!!!
 
pure inductive load , and what about these super conductors in sern


my questioning comes from a lack of understanding on my part not questioning yours but as i was taught

Ib = P/(400x1.732xpf) example 10kW so 10,000/(400x1.732x0.8)= 18.04

selection of protective device

In= 20A

then It = In/rating factors ca cg etc

then on to VD

mVxIxLoR/1000
 

Reply to Help with three phase power in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I really can't see a problem with it assuming there is a neutral there.
Replies
6
Views
498
  • Question
Probably a bit late for the OP, but there's a very easy option if a manual solution is OK. Rotary cam switches are just the ticket - but not the...
Replies
4
Views
570
  • Question
Agree with Dave disconnect unused Phases on the outgoing side of the isolator. No reason to replace mcbs with single pole, unless you need room...
Replies
2
Views
1K
  • Question
Had this before, found by the DNO to be a corroded fuse carrier on a pole mounted fuse on their LV network
Replies
1
Views
665
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks