9.5KW shower at 240V takes 39.6A
9.5KW shower takes 37.9A at 230V
40A Circuit Breaker will hold indefinitely for a 9.5KW shower.
Will not trip what ever you have to do in the shower.
The debate is that some people believe 6mm cable is adequate for a 40A MCB, not that a 40A MCB is ok for a 9.5 kw shower.
Supply Voltage = 230 Volts
Power factor = 1
Ib - Design current = 41.3 Amps
Protective Device Type = MCB type B (BS EN 60898)
In - Protective Device Rating = 45 Amps
Cable Type : Twin & Earth
Length of run of cable = 10 metres
Installation Method : Single-core or multicore cable direct in masonry having a thermal resistivity
not greater than 2 K.m/W - without added mechanical protection.
(method C)
Ambient temp = 30 °C
Number of circuits including this one = 1
Length of cable in thermal insulation = none
Apply Correction factors:
From TABLE 4C1 : Cg = 1 (Grouping)
From TABLE 4B1 : Ca = 1 (Ambient temp)
From TABLE 52.2 : Ci = 1 (Insulation)
Protective device factor for Buried cables : Cc = 1
Cd = 1
Cs = 1
Protective device factor : Cf = 1
It = tabulated current carrying capacity
It = In / (Cg x Ci x Ca x Cf x Cc x Cs x Cd)
It = 45 / (1 x 1 x 1 x 1 x 1 x 1 x 1 )
It = 45.00 Amps
From TABLE 4D5 Cable selected = 6 mm²
Current capacity of cable selected = 47 Amps
TABLE 4D5 For 6 mm²: mV/A/m = 7.3
mV/A/m corrected for power factor = mV/A/m x Power Factor = 7.3 x 1 = 7.3
Voltdrop = (mV/A/m x Length x Design current) / 1000
Voltdrop = ( 7.3 x 10 x 41.3 ) / 1000
Voltdrop = 3.01 Volts
(Maximum permissible voltdrop (regulatuon - 525) = 11.5 Volts)
Calculated Cable size = 6 mm², Actual Earth conductor size = 2.5 mm²
Maximum Cable Length = 38.1 Metres
Power factor = 1
(method C)
Cd = 1
Cs = 1
It = 45.00 Amps
Haha!! I wondered if someone couldn't resist posting the calculation !!
Just out of interest, I would have thought there was a good chance of some cable Grouping (Cg) at some point on the run but i know not always - the original post didn't specify either way. If in doubt i always assume there must be a few cables running together! Just one cable along side would take the requirement above 50A - just a thought!
Also, are there many MCB manufacturers who make a 45A Type B MCB now? If only 50A MCB available then 6mm again, no good.
Thought most modern boards (17th edition etc) only give the options of 40A & 50A. Only seen 45A on old Wylex breakers. You know anyone who supplies 45A MCB's with new RCD boards - be interesting to know for future reference!!??
Power factor = 1
(method C)
Cd = 1
Cs = 1
It = 45.00 Amps
Kenny my friend, you will find that the manufacturer states 9.5KW at 240V and this equates to 8.7KW at 230v.
Therefore the Ib you refer to is 8725/230 = 37.93Amp
Hi Guys,
ive come across this same problem at least 3 times. All caused by 9.5kW showers on 6mm sq pvc/pvc.
The first two occasions, the problem lay in the 45Amp shower isolators, where the neutral conductor at the supply side, had melted the insulation completely, yet the conductor itself, remained intact.
Now the estimated lengths of these circuits(all separate addresses):
one 15m run, one 20m run (wired to 3036 30a fuse).
Now the third problem is the shower which is not yet turned on, as the plasterer has to finish, prior to commissioning of the circuit. The run is less than 5m and ive got the same problem, all for the sake of 1A.
Im going to comission the circuit, which is protected by a 40A breaker, housed with 30mA RCD (shower mcb unit) and ill monitor how it goes by checking the isolator, every so often. An l would suggest everyone else with this issue does the same.
i'd have liked kenny's post if i could reads it, but i've lost my magnifying glass. LOL.
Recommend upgrading to 10mm for sure, who knows what the cable is running through or under. In my opinion, if its borderline then it's wrong. No room for maybe's in this game..
I'm putting a new shower circuit in today. Here's how I ensure method C, by maintaining an air gap around the cable where it passes through the insulation layer.
This isn't finished yet. There's a Crabtree shower pull below that joist and there's another cable to put in yet.
I've left slack in the cable above the isolator just in case the cables should ever need reterminating. To reduce the chances of that happening the ends are treated with cord end ferrules which stop the strands spreading and improve the quality of the connection.
Nice fabrication!
Well done!
At last! Someone else who undestands the shower ratings and the effects of Ohms Law when the voltage is reduced!
Except that I think you made an arithmetic error:
(9500 x 230) / 240 = 9100kW
Ib = 9500/240 = 39.6A
or
Ib = 9100/230 = 39.6A
So, fine on a 40A for non-continuous use (or leave a space on at least one side of the MCB)
Nice fabrication!
Well done!
Thanks. It takes less than 10 mins to cut that out of soil pipe and just a couple of minutes to install. There's a similar arrangement at the other two points the cables pass through the insulation. And the battons are simply screwed to the roof frame uprights.
This method also has the advantage of minimising the disturbance of the insulation and creating less 'fibre-gas'.
And, yes, it's a 9.5kW shower on a 40A MCB.
I understood that we had professional Electricians on this forum, who could at least use the Ohms Law!!!!
You have proved me wrong.
Here is my proof :-
Power=VxV/R
Rated power for the shower @ 240V is 9500W
R is the shower heater resistance
@ 240V, R = 240x240/9500W = 6.063 Ohms
Shower Ohms are constant at all volts, but the supply volts change to 230V
Power = VxV/R @ 230V =230x230/6.063 = 8725 Watts
Load Current @ 230V = Power/Volts = 8725/230 = 37.93Amps