P
pete555
remember you have to satisfy loop impeadance values to protect from over current
I don't agree with the statement that the ground consolidates especially when (very rarely) we have a long dry spell and the ground starts to crack and gaps appear. I realise the rod is 1200 mm long and the ground won;t dry out for the full depth but it could go down about 300mm thus reducing the contact with the rod.
This is where we disagree. I think they're perfectly suitable and defines the needs of a TT system quite clearly. The only bit I'm not quite sure on is the 200 ohms? Seems like a randomly generated value and in my opinion should be replaced with a calculation.
Really?? We must be looking at completely different versions then ...lol!!
And this type of remark helps no one. If I didn't like you and respect your knowledge I would be calling you an arrogant twit right about now![]()
This is fundamentally the problem, where most of you sparks go wrong right from the word go. You will never achieve any form of stability with a single 1.2m rod of any size, and that's a fact!! I have no idea why in fact earth rods were ever reduced from what they used to be, (8 and 10 foot X 5/8'' /3/4'') to these tiny 1.2m lengths you have now. You Need a good 8' of rod in the ground whenever possible, or there isn't going to be any stability in the system!! Fortunately depth also reduces a rod positions Ra value too, so it's the way to go!! So don't use a single 1.2m rod for a TT system, always use at least 2 X 5/8'' rods coupled together with a coupler as an absolute minimum....
So you don't believe that the ground/soil consolidates around an earth rod over time?? Perhaps you don't believe in ground settlement either?? It's a fact i'm afraid!!
Nothing arrogant in that statement at all
I installed a rod a few weeks ago at a sewage plant serving a pub...(following on from an EICR). The reading from the existing spike was 700 odd ohms,no idea what the rod was as it was completely buried. Replaced it with a coupled rod beloved of E54 and got something like 15 ohms....happy days. But let me state now I'd have been just as happy with 115.
Why everyone keeps banging on about the importance of stability is another thing that defeats me.....yes,if you are going to rely on a low enough Ra to operate an OCPD the stability is vital....if your Ra means one or more RCD's are needed for earth fault protection why does stability matter?....it can be 10 ohms or 500....the RCD will still trip the same.
I think this is where the 'plucked out of the air' 200 ohms figure has been arrived at.....Ra values below that are not likely to exceed the 500/1667 value required for safe operation of RCD's even if ground conditions change.
I 've installed a few of these in my early days didn't put many 8ft ones in though about 3 I think.
they used to be terrible if you hit a bit of stubborn ground. the steel cap that was screwed on to help not deform the top of the rod didn't always work,
We were putting these in when voltage operated trips were the norm. That was because there was a higher current in the main earth when a fault occurred. Not long after they were outlawed(Voltage trips) it was decided the rods did'nt need to be that big because of the smaller current needed and the speed of the R.C.D.
As for the ground consolidating I've been on some rewires where I 've pulled the old rod out of the ground with little or no resistance. So I stand by what I say.
One thought though is why the pulled out easy in the first place. Could this have been the installers fault?
Firstly not all TN circuits will have RCD protection,and secondly there are maximum Ze values for TN systems,therefore if a Zs reading was considerably higher than the maximum for a standard OCPD something is clearly not right.That said I would have no problem relying on an RCD to meet disconnection times wher a type B needed to be changed for a type C/D and Zs slightly exceeded the max permitted value.
As I've already stated...if you achieve a TN value of Ra I'm with you all the way......but thinking 10...20...30 ohms is any better than 100-200 ohms ,I'm not.
engineer 54, from day 1 of my apprenticeship it was drummed into me that the regs are the electricians bible and even though they are not a legal document they can be used in a court of law.
So if the regs recommend that a circuit be installed in a certain way, then it is probably advisable to follow them.
We have been treat like sheep from day 1 and to deviate from this path would be a tad risky, in thatif something went wrong through no fault of your own you could find yourself up s...t creek without a paddle
Rumour has it that the rod length was shortened so all those DI's could get the shorter rods into their ex-company carsI have no idea why in fact earth rods were ever reduced from what they used to be, (8 and 10 foot X 5/8'' /3/4'') to these tiny 1.2m lengths you have now.
much more of this thread and i will be tempted to bang a scaffold pole in the garden, hopefully will miss the incoming cable, gas main, water main , and drains. aiming for a Ra comparable to the Ze i've already got from a 951 on the lead sheath. :ack2: