Hello,
I would begrateful for some advice.
I have recently moved into a property which has two detached outbuildings, one used as a garage and the other as a workshop, no heavy machinery just the run of the mill drills and saw.
The outbuildings are connected to the house in this manner;
From main ConsumerUnit, 80A / 30mA RCD via a 32A MCB to the Garage Consumer Unit,63A / 30mA RCDvia a 32A MCB to the Workshop Consumer Unit, 40A / 30mA RCD. The circuit is earthed via an earth rod ouside the house.
What I would like to know is does this meet the existing requirements or is it an overkill?
I am not after technical details as I intend to contact a local electrician. What I will be grateful for is some information, if this set up does not meet standards, so that I can have an idea for when I get the quotes.
Kindregards
Take a few photo's of your 3 X consumer units, preferably with the covers removed so that we can see what you actually have. We can then recommend the best way to go ahead with as to, what to ask the electrician to quote against...
I would however recommend, that you do install an earth rod (2 X 5/8'' coupled together for depth) at each of the 2 outbuildings as a matter of course. Connecting these 2 additional rods with the house's main rod will not only serve the two outbuildings, but also lower the overall Ra value, which serves the main house installation too!!
Graet, thanks for that. I will upload photos ASAP. As forthe coupled rods, I should be able to do that without hitting any services, that is if the drawings are right.
just out of interest...where is that rod sited in relation to the building?
To put things into context, the building is a bungalow. The rod is not copper but looks like steel, how long it is I don’t know. It is situated about six inches from the wall.The earth cable goes through the wall up the cavity to the CU. The overall distance from the rod to the CU is 12 to 15 ft. I intend to have a further two rods fitted, of the type suggested by Engineer54, one outside each of the outbuildings.
come at least 4ft. from the building/s. that will miss the rubble that the idle builder has buried, and use a decent earth pit.
what he`s on about is getting several 5/8" rods and connecting them together to form one long rod.....you dig a pit first as Tel says...this is to ensure you arn`t going to hit any buried services with any rods you drive into the ground....once you have dug the pit and are sure you wont intercept any pipes and/or service cables etc...then you drive the first rod in.....then you connect the second rod to the first and carry on drivin it in...this is what eng is saying about stable Ra values being obtained....
depth is key with TT.....
Thanks, yes I can manage that. So basically the system is OK with 3 CUs but the following needs to be upgraded:
  1. The 32mA MCB in the main CU to 40mA.
  2. The earthing system
Will this work constitute ´new works´ and affect the whole circuit from the main CU to the workshop and as a consequence require the whole circuit to be replaced to present standards?
Mittel, first post up the photo's on here, then we can advise as to what options your going to have, that can be quoted against with your electrician. The first thing you can ask him to provide, is the measured Ra value of your existing earth rod.
What sort of distances are we talking about, between the main house and the two outbuildings??
I appreciate that you are limited as to what advice you can give and that photos of the system will give you a better idea however, I’m not very good at uploading /downloading gizmos so I’ve asked my daughter to come over and do it for me.
As for the distances, the garage is about 4 meters from house and the garage to the workshop, CU toCU, is about 35 meters.
I have been informed that if I contact the distribution company they will do an earth test and if needed fit a "Protective MultipleEarth"
not if the existing cable etc. are in safe condition and "fit for continued use".
ll there is power and light in the two outbuildings and the preious owner run it as a proper workshop with lathe and a number of other woodworking machinery,but that is not to say that it is "fit for continued use". So that´s another one on my list to discuss with the electrician. Many thanks.
reason CSA has been asked here and length of run is for volt drop.....
thats why their askin....
That would be the better option as far as system earthing is concerned, but may also involve you having to run a new supply cable to either one or both of the outbuildings if they have any extraneous earthed services within them, such as a metallic water service pipe. In order to comply with PME requirements you'll need a 10mm bonding cable connection between the main house MET and the bonded pipework. Which can be via a single 10mm bonding cable, or a new 10mm 3 core SWA cable replacing the existing cable.
I remember you saying that the existing supply cable was a 10mm T&E in heavy wall conduit/pipe, if the pipe is large enough, then the single 10mm cable can be pulled into this existing pipe....
rods more cost effective here eng....and if he gets it right with them.....
There are no other services to either the garage or the workshop. The workshop is of timber construction with tiled roof and the garage is standard brick.
Ipswich
Electric connections to outbuildings
Mittel,
Engineer54,