Hi all. Just went to a property where the water and taps were given a shock to the house occupiers. The boiler was cross bonded and had a bonding conductor run to the MET. But however surprisingly the property did not have the main earth. So I had connected a 16mm earth to the ccu and when I was connecting it to the met, it went bang when the 16mm came in contact with the met and let off a little spark. What could this be? The electric was on while I done it, the occupier a has relatives over so could not turn it off.
 
But what test could I have done if the fault wasn't there at the time I was at the property. You could only test something when the fault is present. No safe isolation wasn't done it was only connecting a earth. We all do a quick fix on a Sunday evening it wasn't dangerous it's all in good working condition
 
Live taps sound bloody dangerous too me, the earth going bang when you put it I to the MET sounds dangerous to me, a house without a main earth sounds dangerous to me.

Did you test what voltage on the taps?
did you test for voltage across the terminals at the DB.
Why didn't you carry out a global IR?

sounds like someone has borrowed a earth for a neutral somewhere.
 
Live taps sound bloody dangerous too me, the earth going bang when you put it I to the MET sounds dangerous to me, a house without a main earth sounds dangerous to me.

Did you test what voltage on the taps?
did you test for voltage across the terminals at the DB.
Why didn't you carry out a global IR?

sounds like someone has borrowed a earth for a neutral somewhere.
no...not necessarilly...

sounds like cable/s in contact with hot pipework...

to the OP:

Kiill the power at the incomer...

IR test between each final at the dis-board and pipewirk to verify which circuit is the offender...
 
I would go back to the property apologies and say you need to carry out further tests if the install is a TNCS there is a possibility of a supply fault hence the reason they were getting shocks on the taps, in the event of a fault it doesn't matter if the queen is there you need to carry out safe isolation and the basic tests , start at the beginning quick Ze for starters and works your way round
 
There's a possibility of a supply fault but it's a long shot compared to the problems being on the consumer side. As stated sort out the main earth fault(s) and test the incoming supply first followed by bonding where necessary followed by testing the circuits etc. There's a good chance there's going to be more than one fault so be methodical and don't skip anything.

The installation is very unsafe at the moment so it needs immediately isolating to prevent someone getting injured. If you're even a little unsure of the testing procedure please get assistance from someone with more experience.
 
There's a possibility of a supply fault but it's a long shot compared to the problems being on the consumer side. As stated sort out the main earth fault(s) and test the incoming supply first followed by bonding where necessary followed by testing the circuits etc. There's a good chance there's going to be more than one fault so be methodical and don't skip anything.

The installation is very unsafe at the moment so it needs immediately isolating to prevent someone getting injured. If you're even a little unsure of the testing procedure please get assistance from someone with more experience.
you can have a like for it...even though you banned me you snotty gyt...:tongue:
 
Thanks Glenn, I'm not one to hold a grudge either for your pic in the general forums :)

Seriously though with this kinda thread the thing that worries me is it's very easy to jump on the guy and give him hell but if he was lacking in confidence and thinking about getting someone to assist him on site then getting a load of flak is likely to reduce the possibility of this happening.

I agree with Voltz as well a spark is very likely given that the earth is functional as well as protective but the word 'bang' kinda suggests a more sinister problem.
 
Thanks Glenn, I'm not one to hold a grudge either for your pic in the general forums :)

Seriously though with this kinda thread the thing that worries me is it's very easy to jump on the guy and give him hell but if he was lacking in confidence and thinking about getting someone to assist him on site then getting a load of flak is likely to reduce the possibility of this happening.

I agree with Voltz as well a spark is very likely given that the earth is functional as well as protective but the word 'bang' kinda suggests a more sinister problem.


but then he just thought `f**k it`...i`ll just crack on anyway....

- - - Updated - - -

Thanks Glenn, I'm not one to hold a grudge either for your pic in the general forums :)

Seriously though with this kinda thread the thing that worries me is it's very easy to jump on the guy and give him hell but if he was lacking in confidence and thinking about getting someone to assist him on site then getting a load of flak is likely to reduce the possibility of this happening.

I agree with Voltz as well a spark is very likely given that the earth is functional as well as protective but the word 'bang' kinda suggests a more sinister problem.
lol.....lol..
 
Hi all. Just went to a property where the water and taps were given a shock to the house occupiers. The boiler was cross bonded and had a bonding conductor run to the MET. But however surprisingly the property did not have the main earth. So I had connected a 16mm earth to the ccu and when I was connecting it to the met, it went bang when the 16mm came in contact with the met and let off a little spark. What could this be? The electric was on while I done it, the occupier a has relatives over so could not turn it off.

Erm.....you need to grow a pair and start putting the safety of your customers first.
 

Reply to Earth goes bang! in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top