Hi guys.
I am in a.bit of a tiz with this one, an external light with no built-in fuse carrier is required to be fed by a 16A socket backed up by a 16A rcbo due to the fact the socket will some time be used to supply a heavier load. What about over current protection of the light.
 
As above, probably what I would do is metal-clad FCU and a couple of plastic glands to grip the cable. Could be switched if you need a operational switch somewhere, otherwise just fuse only.
 
Hi guys.
I am in a.bit of a tiz with this one, an external light with no built-in fuse carrier is required to be fed by a 16A socket backed up by a 16A rcbo due to the fact the socket will some time be used to supply a heavier load. What about over current protection of the light.
As a fixed load it doesn't require overload protection, but does require fault current protection, so providing the cable supplying the light etc is suitable for protection by 16A it is completely acceptable as is....

Unless the luminaire has a note stated "this must be protected by a 6A mcb" or similar, in which case fit a fcu with a 3A fuse between the plug and luminaire.
 
'Fixed load' was being used to mean 'unable to create an overload condition'' rather than 'fixed in position.' A lamp generally cannot cause an overload so as per @Julie. it does not need overload protection. If the lamp were somehow able to draw 3A it would be on fire, so there is no point fusing the 16A supply down to 3A to protect against overload as it won't. Therefore only fault protection would benefit and that is more or less down to the choice of cable unless the MI's state otherwise. Wire it in 1.0 sq, mm and there is no point fusing that down below 16A either.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Kent
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
16A socket with 3A load
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
Pingpong,
Last reply from
Lucien Nunes,
Replies
6
Views
2,174

Advert

Back
Top