KEVINDOE

Morning all,

I have a shop at first fix stage, there are two ring final circuits, three lighting circuits, the lighting circuits are all downlighters and the cabling for the circuits including the rings are all in stud walling as original walls have been battoned off.
The shop has been empty for a while and the original tennant had all supplies ripped out, exept for the c.u.which is 16th edition.
My question is, do the lighting circuits need to be r.c.d,?..or could all circuits be on the r.c.d. side as it is commercial ?

Thanks in advance
 
If it was my decision, for the sake of 5 circuits, I'd just use RCBO's and then you're covered for use by skilled/instructed/non instructed persons, cables buried in walls at depths of less than 50mm etc etc.
 
Yes Dave.. main switch already there so i think i will alter the box and add another r.c.d. ....sorted ...thanks for all the replys lads :)
 

Reply to 16th edition in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock