Discuss Spds - multiple consumer units in the UK Electrical Forum area at ElectriciansForums.net

In my opinion if you have distribution boards downstream a reasonable distance from the other distribution boards then these really should have their own SPD as well. One at the origin won't cut it.
When a sub-distribution board is located more than 10m away from the mains SPD, additional SPDs are required.
Both his consumer units are close together.
It leaves the question of does the garage need one.
 
Last edited:
Could someone kindly share why the SPD unit must be in parallel? I'm confused sorry! Hard to say without a basic wiring diagram of the current installation.
I assume a plastic 100A isolator switch with a built in SPD would work straight after the main supply incoming tails. Then anything downstream will be protected, including the time delayed RCD and all the other CCUs. . Though not strictly allowed (dno only), but could be placed in the meter cabinet. Here are examples:

Wylex type 2 SPD isolator, suitable for TT


There may already be an isolator after the main tails not sure. But that could be replaced with this.
 
Last edited:

Reply to Spds - multiple consumer units in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top